Re: [EnergyPlus_Support] Window simulation
What specific window properties did you change? In EnergyPlus
MATERIAL:WINDOWGLASS, you specify reflectances and transmittances, and the
remaining solar energy is absorbed in the glass. With all other inputs equal,
a lower transmittance will result in higher absorptance which will increase the
glass temperature and offset some of the benefits of the lower transmittance.
Perhaps it would help to report the surface temperatures and other window-
related report variables both models to help explain the results.
Mike
On 17 Nov 2006 at 16:22, ronald_borduni wrote:
> Hi,
>
> in my simualtion, i tried to change the glass of the windows on my
> building for glass with less solar penetration, in fact to minimize
> the thermal load. But the result i heve is a increase of 1% in my
> thermal load, besides the decreasing i expected.
> I've made some tests like remove the windows, to see what happens, and
> the thermal load reduced considerably. So, i think i hadn't declared
> wrongly the windows, but i don't know what's going on.
> Can someone help me?
> Thanks,
>
> Ronald.
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/