Hi all: I have a problem with the chillers control, we set up two 
chillers totally, and there are three operation schemes: 
scheme1: only the little chiller runs when the demand load is small;
 scheme2: the bigger one begins to run as the demand load becomes 
enough large;
scheme3: the little chiller and the bigger one run together when the 
demand load becomes more;
The problem is that how to set up the value in the COOLING LOAD 
RANGE BASED THE OPERATION?  What is meaning of the Load Range Lower 
Limit 1 and the Load Range Upper Limit 1 values?
1.	for scheme 1, is Load Range Lower Limit 1 is equal to zero? 
And is Load Range Upper Limit 1 equal to the nominal capacity of the 
little chiller?
2.	for scheme 2, is Load Range Lower Limit 1 equal to the 
nominal capacity of the little chiller? And the Load Range Upper 
Limit 1 equal to the nominal capacity of the bigger chiller?
3.	for scheme 3, is Load Range Lower Limit 1 equal to the 
nominal capacity of the bigger chiller? And the Load Range Upper 
Limit 1 equal to the sum of the bigger chiller nominal capacity and 
the little chiller nominal capacity?




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/