Conductance is Conductivity divided by thickness, but this will give you the
conductance of just the glass (and gas) layers only. I presume that the U-
values you are referring to also include the inside and outside film
(convection) coefficients as well. If they are from Standard 90.1 (or 90.2)
they use the film coefficients for a specified set of temperature and wind-
speed conditions. EnergyPlus will report this standard U-value in "Report,
Surfaces, Details;" See Output Details and Examples document, p. 23, pdf p.
29, for more information. You will need to use the film coefficients shown
here, remove them from the U-value, then calculate the thermal conductivity
that will result in the desired U-value.
Mike
On 26 Dec 2006 at 22:54, kevinzmo wrote:
> We're simulating a series of windows with different U-values
> (conductance, w/m2-k). But the input of WindowGlass requies
> Conductivity (w/m-k). How do we deal with it?
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/