Re: [EnergyPlus_Support] Re: Without PurchasedAir?



ooi,

Both the reduction in peak temperature (inside vs outside) and delay in 
the response
are what is expected from thermal mass effects. If you didn't see this, 
there would
be cause for concern.

Fred Buhl

ooikoonbeng2004 wrote:
> Thank you Linda and Brent, i did not study enough when i asked. 
>
> With 1zoneuncontrolled, or setting the PurchasedAir to LIMIT with 
> zero as the limit, inside air temperature shows less fluctuations 
> than outside air. Also there is a time lag as the inside air temp 
> tries to follow the outside air temp, especially in the afternoon. 
> Correct me if i am wrong, i attribute this to the thermal mass of 
> the construction (from materials without the R) of the building.
>
> regards
> ooi
>   --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Linda Lawrie 
> <linda@...> wrote:
>   
>> Look at the 1zoneuncontrolled input file.
>>
>> All you need are the building objects.  you probably should remove 
>> all the schedules, people, elec eq, etc statements as well as the 
>> HVAC related ones.
>>
>>
>> Linda
>>
>> EnergyPlus WebSite: http://www.energyplus.gov
>> Owner: EnergyPlus_Support list
>> Member: EnergyPlus Development Team
>>
>>
>>
>> [Non-text portions of this message have been removed]
>>
>>     
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
>  
> Yahoo! Groups Links
>
>
>
>   


[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/