Re: [EnergyPlus_Support] Re: Psychrometric Error
Yes, you are misinterpreting the error message - which isn't surprising,
given that
the messages are very hard to interpret. The error messages are coming
from the
psychrometric routines - which are used in many places in the program.
The problem
has nothing to do with the weather file. Instead it is the DX coil model
itself that is
the probable source of the error. But we can't tell for sure since the
psych error messages
don't indicate where the psych routines were called from. Most likely
the problem arises
from your curve fits. To figure out what is going on you will have to
upload your
input files for us to run.
Fred Buhl
brianstreby wrote:
> Converted my weather file to .csv format and looked up data for
> 04/01. everything appears normal. since the out-of-range data is
> occurring at an interval between 10:00 and 11:00, isn't it likely
> that this is a programing bug? perhaps i am misinterpretting the
> warning? my specific errors are as follows:
>
> ** Warning ** Enthalpy out of range (PsyTsatFnHPb)
> ** ~~~ ** Occurrence info=WILKES-BARRE PA USA TMY2-14777
> WMO#=725130, 04/01 10:10 - 10:20
> ** ~~~ ** Enthalpy=-159923.52524 Pressure= 99366.66
> ** ~~~ ** Initial Resultant Temperature= -59.98
> ** Warning ** Temperature out of range [-100. to 200.]
> (PsyPsatFnTemp)
> ** ~~~ ** Occurrence info=WILKES-BARRE PA USA TMY2-14777
> WMO#=725130, 04/01 10:10 - 10:20
> ** ~~~ ** Input Temperature=-176.56
> ** Warning ** Temperature out of range [-100. to 200.]
> (PsyPsatFnTemp)
> ** ~~~ ** Occurrence info=WILKES-BARRE PA USA TMY2-14777
> WMO#=725130, 04/01 10:10 - 10:20
> ** ~~~ ** Input Temperature=-176.93
> ** Warning ** Temperature out of range [-100. to 200.]
> (PsyPsatFnTemp)
> ** ~~~ ** Occurrence info=WILKES-BARRE PA USA TMY2-14777
> WMO#=725130, 04/01 10:10 - 10:20
> ** ~~~ ** Input Temperature=-176.95
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "brianstreby"
> <brianstreby@...> wrote:
>
>> I have a similar issue. I ran the "Weather Statistics and
>> Conversions" program and asked it to fix out of range data, but
>>
> still
>
>> end up with out-of-range enthalpy and temperature data for the
>>
> 04/01
>
>> 10:10 - 10:20 time segment.
>>
>>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/