Arno:

The situation you describe cannot exactly be modeled in EnergyPlus.  What 
can be done is to have both the radiant system and the purchased air system 
turn on at 23C with the radiant system taking priority over the purchased 
air system.  Unfortunately, any load not met by the radiant system will be 
met by the purchased air system, even if the temperature is not yet above 26C.

Currently, we are looking at the possibility of changing the radiant system 
controls.  The biggest change being considered is the decoupling of the 
radiant system from the thermostat controls used for conventional forced 
air systems.  If such changes are implemented, then you would be able to 
achieve the control that you described in your email.  This is something 
that the development team will discuss and prioritize for work in the near 
future.

Thanks,

Rick Strand
EnergyPlus Development Team


At 01:58 AM 2/14/2007, you wrote:


>Hello.
>
>Is it possible to combine/control a LOW TEMP RADIANT SYSTEM:HYDRONIC
>with a purchased air (cooling) object in this manner:
>
>1. start cooling with low temp radiant system above 23 °C (MAT)
>2. start (second) cooling with the purchased air object if the room 
>temperature is above 26 °C
>
>At the moment both objects starts if the room temperature of the ZONE 
>CONTROL:THERMOSTATIC is
>above the setpoint.
>
>Ideas are welcome.
>
>Regards, Arno


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/