[EnergyPlus_Support] Mixed air setpoint manager -- bad mixed air setpoint calculation
My mixed air setpoint manager is calculating a very low setpoint, i.e.
less than freezing, subsequently causing the economizer to suck in
lots of cold air in the winter.
For the first ten minute time step on Dec 15, relevant system node
temperatures are as follows:
Outdoor Dry Bulb [C]: 1.7
Return air temp[C]: 13.2 (after return fan)
Mixed air setpoint temp [C]: -5.3 <---------- !!!
Mixed air temp [C]: 1.7
Supply fan inlet temperature [C]: 1.7
Supply fan outlet temperature [C]: 1.9
Temperature at reference setpoint node[C]: 12.7
Question 1: What could possibly cause this?
Question 2: I am usig 6 time steps per hour and noticed big
fluctuations from one time step to another for a number of output
variables. What could be causing this instability?
Many thanks,
Brian
------------------------ Yahoo! Groups Sponsor --------------------~-->
Great things are happening at Yahoo! Groups. See the new email design.
http://us.click.yahoo.com/lOt0.A/hOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups - Join or create groups, clubs, forums & communities. Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups - Join or create groups, clubs, forums & communities. is subject to:
http://docs.yahoo.com/info/terms/