First, you do not need airflow network objects to model this. That is an
advanced feature that should be added only after the rest of the HVAC system
model is in place and working properly.
EnergyPlus can model DOAS by using an AIR PRIMARY LOOP with DIRECT AIR terminal
units to deliver preconditioned outside air directly into one or more zones.
Then a zone equipment system, such as fan coil or PTAC or PTHP is used to meet
the net zone load. Be sure to list the DIRECT AIR units with priority = 1 in
the ZONE EQUIPMENT LIST. There is no example file like this.
Mike
On 21 Feb 2007 at 5:58, love9787m wrote:
> Dear Sir
>
> I'm currently working on a project which makes DOAS using enegyplus
> But I'm beginner, now I have a lot of difficulties to figure out DOAS
> in enegyplus.
> First, I made a simple building using designbuilder and exported to
> energyplus and then to figure out the DOAS, enter the value at the
> items (airpath, airflow network system, etc) and ran the simulation
> But I found errors
> Considering those process, I made a lot of mistakes.
> Now I'm tired to find the way which figures out DOAS.
> Please Let me know about process, items which should be filled.
>
> Sincerely,
> Dae Woong Ha
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
See what's inside the new Yahoo! Groups email.
http://us.click.yahoo.com/0It09A/bOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/