You must add an HVAC system to control to the set point if the loads are 
to be meaningful. I recommend using the Compact HVAC:Zone:Purchased Air 
system and to also use the Compact HVAC:Thermostat object. These compact 
HVAC objects make it much easier to set up the system.

jeongch1004 wrote:

> Result is follow as shown.
>
> OutdoorDryBulb[C] /ZoneMeanAirTemp./ "Zone/SysSensibleLoadPredicted
> [W]"/"Zone/SysSensibleLoadtoHeatingSetpointPredicted[W]"/"Zone/Sys
> SensibleLoadtoCoolingSetpointPredicted[W]"
>
> 4.033333333/ 8.978055754/ 0/ -852.6063832/ 853.8331622//
> 4.525/ 8.966831774/ 0/ -851.6064025/ 852.8752779//
> 4.283333333/ 8.950181543/ 0/ -851.582205/ 853.2167353//
> 4.083333333/ 8.933127341/ 0/ -851.9443016/ 853.5446422//
> 3.883333333/ 8.916201903/ 0/ -852.2052171/ 853.8277879//
> 3.625/ 8.898818409/ 0/ -852.5261543/ 854.190358//
> 3.383333333/ 8.881014555/ 0/ -852.9178424/ 854.6223443//
> ./ ./ ./ ./ .//
> ./ ./ ./ ./ .//
> Continue as similar pattern
> I selected "Dual setpoint-", heating setpoint is 20(C), cooling
> setpoint is 26(C)
> Zone Mean Air temperature range from 8 to 35, but "Zone/Sys Sensible
> Load Predicted[W]" indicated 0 (all), Zone/Sys Sensible Load to
> Heating
> Setpoint Predicted[W]" is negative value(all), Zone/Sys Sensible Load
> to Heating Setpoint Predicted[W]" is positive value(all).
> Why did I get result like this?
>
>  


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/