Re: [EnergyPlus_Support] Compact HVAC:Zone:FAN COIL



There is no such equipment type in EnergyPlus.  For cooling, you should be able 
to set the performance of an air cooled electric chiller to match the heat pump 
performance, see example file 5ZoneAirCooled (but I would recommend using 
CHILLER:ELECTRIC:EIR rather than CHILLER:ELECTRIC).  For heating, I suppose you 
could use the heat pump water heater (HEAT PUMP:WATER HEATER) with the heating 
coils supplied from the "Use side" of the WATER HEATER:MIXED object.  See 
example file HeatPumpWaterHeater.  This contains 5 different heat pump water 
heaters, with one configured to serve a space heating hot water loop, the 
"Plant" HPWH - see comments at top of example.

Mike


On 30 Mar 2007 at 11:26, Emanuel Sá wrote:

> I have one other question. This fan coil system is fed by a reversible
> chiller that works as a chiller during the cooling season and as a heater
> during the heating season. I couldn't find a plant equipment such as Heat
> Pump Water to Air. Is there any possible way to simulate this kind of
> system? I've read a previous post(2005) on this subject, and it was said
> that at that time that couldn't be done. Is there a way to do that now?


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/