[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: About two system combination?
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@...> wrote:
>Thanks anyway. I think your advice will be helpful.
> I am not sure I understand the question completely.
>
> To model a DOAS plus fancoil unit serving the same zone. Use an
AIR PRIMARY
> LOOP with DIRECT AIR to model the DOAS, and zone equipment FAN
COIL UNIT:4 PIPE
> to model the fancoil unit (see example file FanCoilAutoSize.idf).
To simplify
> setting up the fan coil units, you could use COMPACT HVAC:ZONE:FAN
COIL to set
> up the fan coil unit(s), then merge the expidf file with the DOAS
description,
> add the DIRECT AIR units to the ZONE EQUIPMENT LIST with
priority=1 (see
> example file CompactHVAC-5ZoneFanCoil.idf).
>
> Mike
>
>
> On 15 Apr 2007 at 11:22, love9787m wrote:
>
> > Hello Mike.
> > Now, I'm studying on difference between DOAS and VAV system.
> > I already knew the method of DOAS configuration, VAV as well.
> > In case, There is one conditioning zone that is supplied the
> > conditioning air from the DOAS and also is conditioned by
internal zone
> > unit or local unit just like a fancoil unit.
> > Those two systems provide air conditioning separately through
each
> > other ductsystem.
> > After finising configuration of DAOS, then next which object or
field
> > or etc. should I treat?
> > I really absolutely don't know the way or method of the case.
> > Please let me the help.
> >
> > Thank you in advance your support
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf
under the
> > Documentation link and press the "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@...
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/