I cannot say for sure if CondFD will be more accurate or not. If the CTF
algorithm reaches convergence during the warmup days, then it should be
reasonably accurate. CondFD should be able to handle this case as well. But I
cannot say that I have verified and compared anything close to the level of
mass you are modeling. Sorry I cannot be more definite. At a minimum, be sure
that all methods handle the steady-state case appropriately (whether it be
EnergyPlus or other tools). Constant temperature with no solar and no radiant
exchange should result in a UADeltaT case which can be verified by hand. Any
method which does not agree for that will probably not be correct for the non-
steady case.
Mike
On 17 Apr 2007 at 11:35, Emanuel Sá wrote:
> Dear all
>
> I'm simulating a 80 cm thick granite wall building. This is obviously
> a high thermal mass envelope. I know that there are some problems
> regarding the simulation of high thermal mass envelopes. I'm also
> comparing my results with the results provided by TRNSYS for the same
> building. In fact they don't match at all! so I was wondering witch
> solution algorithm should I use. I'm currently using the CTF but maybe
> for high thermal mass, the ConFD is more accurate.
> Can anyone give me some insight about this issue?
>
> Thank you in advance
>
> Emanuel Sá
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/