Re: [EnergyPlus_Support] Autosizing and general E+ procedure
I am surprised that autosizing would add significantly to run time. Sizing
performs a loads-only (purchased air simulation) for each DesignDay, then calls
the systems once-through to size components.
All of the computed sizes are reported in the eio output file and once these
are determined, they are fixed for the entire simulation - nothing is changing
over the course of the year.
The procedure for using hard sizes would be to take the values reported in the
eio ouput component sizing reports and copy/paste them into the idf file,
replacing each instance of "autosize". I doubt that you will find much
difference in run-time between the autosized and hard-sized versions of the
input, but if you do, please send me the input files for further investigation.
Mike
On 20 Apr 2007 at 15:24, maenebraska wrote:
> I understand that it may not be necessary to remove the autosizing
> parameters; however, the run time is too excessive when using the
> system, plant, and zone sizing in the run parameters. Is there a
> reccommended procedure for implementing values in place of the
> autosizing numbers that will allow me to run the model without these
> run control features active? It seems that I should be able to "size"
> the plant once based off of typical equipment parameters for a
> building of some cooling load and keep those parameters for each day
> of the year.
> Is there any critical limiting factors that would keep me from setting
> the coil and cooling tower characteristics constant throughout the
> simulation year?
>
> Thank you in advance?
>
> Dan
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/