Re: [EnergyPlus_Support] Interior Blind - BlockBeamSolar
Arno,
There are several factors interacting under your desired control
strategy. You are deploying your interior blind only when beam +
diffuse solar incident on the window is > 180 W/m2. You should output
this variable so that you can assure that your blind is being properly
deployed. Also, the BlockBeamSolar control uses the input data in the
Material:WindowBlind object, which you have not included in your email
message. The Material:WindowBlind construction must be complete and
accurate enough for EnergyPlus to determine the appropriate slat angle
to block beam when the blind is deployed.
Rob Hitchcock
=========
Arno Dentel wrote:
> Dear Users.
>
> I simulate a simple room with an interior blind. The control type of the
> slat angles is: BlockBeamSolar.
> But in the output (FENSTER_1:Window Blind Slat Angle [deg](TimeStep)) is
> always 0.
> At the end of my mail you can find the specifications of the window
> control
> object out of my idf file.
> Has any body an idea?
>
> Best Regards,
> Arno
>
> !- =========== ALL OBJECTS IN CLASS: SURFACE:HEATTRANSFER:SUB
> ===========
>
> Surface:HeatTransfer:Sub,
> Fenster_1, !- User Supplied Surface Name
> WINDOW, !- Surface Type
> 2003, !- Construction Name of the Surface
> Wand_2, !- Base Surface Name
> , !- OutsideFaceEnvironment Object
> 0.0, !- View Factor to Ground
> ysun_1_11, !- Name of shading control
> , !- WindowFrameAndDivider Name
> 1, !- Multiplier
> 4, !- Number of Surface Vertex Groups -- Number of
> (X,Y,Z) groups in this surface
> 0.32260, !- Vertex 1 X-coordinate {m}
> 0.00000, !- Vertex 1 Y-coordinate {m}
> 0.95517, !- Vertex 1 Z-coordinate {m}
> 3.62740, !- Vertex 2 X-coordinate {m}
> 0.00000, !- Vertex 2 Y-coordinate {m}
> 0.95517, !- Vertex 2 Z-coordinate {m}
> 3.62740, !- Vertex 3 X-coordinate {m}
> 0.00000, !- Vertex 3 Y-coordinate {m}
> 2.54483, !- Vertex 3 Z-coordinate {m}
> 0.32260, !- Vertex 4 X-coordinate {m}
> 0.00000, !- Vertex 4 Y-coordinate {m}
> 2.54483; !- Vertex 4 Z-coordinate {m}
>
> !- =========== ALL OBJECTS IN CLASS: WINDOWSHADINGCONTROL ===========
>
> WindowShadingControl,
> ysun_1_11, !- User Supplied Shading Control Name
> InteriorBlind, !- Shading Type
> 2003_Shaded11, !- Name of construction with shading
> OnIfHighSolarOnWindow, !- Shading Control Type
> , !- Schedule Name
> 180.00, !- SetPoint {W/m2, W or deg C}
> No, !- Shading Control Is Scheduled
> No, !- Glare Control Is Active
> , !- Material Name of Shading Device
> BlockBeamSolar, !- Type of Slat Angle Control for Blinds
> ; !- Slat Angle Schedule Name
>
> ______________________________________________________
>
> Arno Dentel - MEng, Dipl.-Ing. (FH)
> Georg-Simon-Ohm Fachhochschule Nürnberg
> Institut für Energie und Gebäude - ieg
> Keßlerplatz 12
> 90489 Nürnberg
>
> Tel: +49 - 911 - 5880 -1846
> Fax: +49 - 911 - 5880 -5846
>
> E-Mail: arno.dentel@xxxxxxxxxxxxxxx <mailto:arno.dentel%40fh-nuernberg.de>
> web: www.ieg.fh-nuernberg.de <http://www.ieg.fh-nuernberg.de/
> <http://www.ieg.fh-nuernberg.de/>>
>
> [Non-text portions of this message have been removed]
>
>
--
Robert J. Hitchcock, Ph.D.
Lawrence Berkeley National Laboratory
1 Cyclotron Road, Mailstop 90-3111
Berkeley, CA 94720
RJHitchcock@xxxxxxx
530.295.9433 (telecommute office)
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/