[EnergyPlus_Support] Re: Window AC or Unitary - Coil:DX:CoolingBypassFactorEmpirical



Hi Linda, 

A 7.04KW CU-C24CTH National Panasonic air conditioner is used on the 
BS1 zone. i was informed, that the rated air volume is 0.253m3/s. My 
rough measurements with an AirFlow anemometer, was 0.197379, 
0.221949 and 0.235053 for low, med and high fan speeds.

When 0.253 was entered into the Coil:DXCoolingBypassFactorEmpirical, 
many understandable out of range errors appeared. But even if i 
changed to a higher figure to be within the range allowed by E+, 
still a few thousand out of range errors appeared. i shall try again 
in a month's time.

ooi
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Linda Lawrie <linda@...> 
wrote:
>
> Rated Total Cooling Capacity would be the "required" total cooling 
> capacity in an autosized run.  You might need to find a 
manufacturer 
> that has that "rated cooling capacity" for the unit.
> 
> Autosized component results are put on the .eio file.
> 
> 
> Linda
> 
> EnergyPlus WebSite: http://www.energyplus.gov
> Owner: EnergyPlus_Support list
> Member: EnergyPlus Development Team
> 
> 
> 
> [Non-text portions of this message have been removed]
>




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/