RE: [EnergyPlus_Support] HVAC Descriptions



You can serve multiple zones in DesignBuilder with a single unitary system
by selecting an HVAC template using the 'Unitary multizone' compact HVAC
type.  In this case, it is necessary to set one of the zones as being
thermostatic control zone.

Andy

-----Original Message-----
From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]On Behalf Of Michael J. Witte
Sent: 23 April 2007 17:37
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] HVAC Descriptions


I am not sure if there is a way within DesignBuilder to serve multiple zones
on
the same unitary system.

One approach is to delete all of the DesignBuilder HVAC input objects, then
use
COMPACT HVAC:ZONE:UNITARY and COMPACT HVAC:SYSTEM:UNITARY to create a single
HVAC system serving multiple zones, designating one zone to be the control
zone.

Mike


On 23 Apr 2007 at 15:04, msemech wrote:

> Greetings:
>
> A basic question.
>
> I'm doing an energy analysis to ASHRAE 90.1.  We've created the model
> using DesignBuilder (DB), but that doesn't do enough for us with HVAC
> system descriptions.
>
> We understand, in a basic fashion, how to read the IDF files.  We need
> to model a building that has several different "zones" on a constant
> volume-single zone system.  DB creates a separate system for each zone
> of control.
>
> Question: How is each zone "linked" to the HVAC system?
>
> Bruce J. Gustafson
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate
folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
Documentation link and press the "search" button.

Yahoo! Groups Links







The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/