Actually, this won't work if you really want a two-speed supply air
fan. It will only work for a single air flow rate in cooling.
Don Shirey wrote:
> To model a PTAC, I suggest using the window air conditioner object
> along with baseboard heating. See objects:
>
> AIR CONDITIONER:WINDOW:CYCLING
> BASEBOARD HEATER:ELECTRIC:CONVECTIVE
>
> and example file:
>
> WindACAuto.idf (although this example file uses Baseboard
> Heater:WATER:Convective).
>
> A specific PTAC object/model is scheduled to be added to EnergyPlus as
> part of the next release (October 2007).
>
>
> w_jiang78 wrote:
>
>> Through the documentation, I found EnergyPlus models PTHP, but not
>> PTAC, and there is only one option for heating (DX coil heating).
>> Would it be appropriate to use unit ventilator to model a PTAC.
>>
>> Thanks.
>>
>> Ashley
>>
>>
>> The primary EnergyPlus web site is found at:
>> http://www.energyplus.gov
>>
>> The group web site is:
>> http://groups.yahoo.com/group/EnergyPlus_Support/
>>
>> Attachments are not allowed -- please post any files to the
>> appropriate folder in the Files area of the Support Web Site.
>>
>> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under
>> the Documentation link and press the "search" button.
>>
>> Yahoo! Groups Links
>>
>>
>>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/