Re: [EnergyPlus_Support] Conflicting output reports
1. In the zone sizing section of the eio output, the peak temperature and
humidity are the outdoor conditions at which the peak zone load occurs.
2. "Rated Total Cooling Capacity" as defined in the Input Output Reference is
the capacity at ARI rating conditions. Actual cooling output will vary with
changing outdoor and entering coil conditions. None of the Report Variable
names have the term "capacity" in them. Definitions of report variable names
may be found in the Input Output Reference; search for the variable name.
Mike
On 30 Apr 2007 at 22:01, aboyemeplus wrote:
> Hi all,
>
> I am having a hard time reconciling the values of the following
> variables as listed in the .EIO output file and the .CSV files.
>
> 1) Zone Peak Temperature and Specific Humidity
>
> In the "Zone Sizing" section of the .EIO file, listed peak zone
> temperature and specific humidity values are as high as the outdoor
> Summer design conditions. On the other hand, the peak Zone
> temperature and specific humidity values from Report Variable
> reflect the fact that that there is temperature control in the
> model, and are much lower than the values listed in the .EIO output.
> Hopefully, Peak temperature/humidity in .EIO and Report Variable
> don't have the same meaning! If so, can you please explain the
> significance/meaning of the variables in the two reports?
>
> 2) AHU-1 Rated Total Cooling Capacity (gross) [W]
>
> In the "Component Sizing" section of the .EIO file, the value
> corresponding to this variable is listed at 8.816 kW. The peak total
> cooling capacity from Report Variable is about 10.6 kW. Again, why
> the difference? Which report is accurate if the variables have the
> same meaning in both reports?
>
> I have uploaded the input file "p599adm-exp-4-23.IDF" into the
> \problem_submittals\ folder.
>
> Thank you for your support.
>
> Merid
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/