Eric is correct.  This is no automated way to do that.  

However, you should be able to get there simply by specifying fixed flow rates 
in the ZONE SIZING and SYSTEM SIZING objects, using the flow/zone and 
flow/system options.  Then let the HVAC components autosize.  The fixed flow 
rates will decouple the autosizing from actual zone loads, and the rest of the 
system sizing is driven by the supply air flow rates.  I can't remember for 
sure if the zone sizing factor is applied to these values (it is for some 
inputs, not for others), so set the sizing factor to 1.0 for this approach.

Mike


On 9 May 2007 at 18:00, Eric Yang wrote:

> As far as I know, there hasn't been a transfer tool for this
> application.   But it would be nice to have this option in IDF.
> 
> 
> 
> -Eric 
> 
> ________________________________
> 
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of noelcrrl
> Sent: Wednesday, May 09, 2007 5:54 PM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Re: Parametric Study and Autosizing?
> 
> 
> 
> Thanks for the response. Would you know of an easy way to input 
> the "autosized" values from the EIO into the IDF. Inputing these 
> values into the IDF manually seems time consuming and I am looking 
> for an easier way.
> 
> Thanks,
> Noel 
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> , Fred Buhl <wfbuhl@...> 
> wrote:
> >
> > If the energy conservation measures affect the building's zone 
> loads, 
> > then the autosized zone design
> > flow rates will change - and downstream the boiler, chiller, fan 
> etc. An 
> > example would be a different
> > type of window - that would affect the autosizing results.
> > 
> > Fred Buhl
> > 
> > noelcrrl wrote:
> > > Dear all,
> > >
> > > I have completed a baseline building in EnergyPlus. All of the 
> > > equipment in this building was autosized. I plan to model 
> multiple 
> > > energy conservation measures using this baseline building. I am 
> > > concerned that with each simulation run where I model an energy 
> > > conservation measure (add it to the baseline model), the capacity 
> of 
> > > the building equipment (boiler, chiller, fan, etc.) will change. 
> Do I 
> > > have to hard size the equipment (boiler, chiller, fan, etc.), 
> based on 
> > > the values from the baseline model's EIO, for the runs where I 
> model 
> > > these measures? Should I expect the "autosized" capacity of the 
> > > equipment to change with each run? Or, should I expect 
> the "autosized" 
> > > values to remain the same with each run? What is the protocol?
> > >
> > > Thanks in advance,
> > >
> > > Noel
> > >
> > >
> > >
> > >
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov <http://www.energyplus.gov> 
> > >
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> <http://groups.yahoo.com/group/EnergyPlus_Support/> 
> > >
> > > Attachments are not allowed -- please post any files to the 
> appropriate folder in the Files area of the Support Web Site.
> > >
> > > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf 
> under the Documentation link and press the "search" button.
> > > 
> > > Yahoo! Groups Links
> > >
> > >
> > >
> > >
> >
> 
> 
> 
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/