[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: Hot Water Reset Savings?
Hi Mike...thanks for the response...
I am having the same issue with chilled water reset...is this to be
expected?
Noel
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@...> wrote:
>
> No, BOILER:SIMPLE does nothing more than apply the nominal
efficiency and a
> part-load curve. It does not model any jacket losses, and so it's
efficiency
> is not sensitive to the supply temperature. Also, with no piping
losses in the
> simulation, that effect is not present either. So, I would expect
the same
> boiler energy consumption for these two cases.
>
> I can't think of an easy way to model this with current
capabilities.
>
> Mike
>
>
> On 1 Jun 2007 at 2:44, noelcrrl wrote:
>
> > Dear All-
> >
> > I am tying to estimate the energy savings of implementing a hot
water
> > reset as a function of outside air. The object was entered as
shown
> > at the end of this message. When I implement the hot water
reset,
> > the energy consumption of the boiler does not change-no energy
> > savings. Why is this the case? Does the boiler:simple object
take
> > into account water delivery temperature into its energy
consumption
> > calculation?
> >
> > SET POINT MANAGER:OUTSIDE AIR,
> > Hot Water Loop HW Temp Manager, !- Name
> > TEMP, !- Control variable
> > 82.2, !- Set point at outside low {C}
> > -6.7, !- Outside low {C}
> > 65.6, !- Set point at outside high {C}
> > 10, !- Outside high {C}
> > Hot Water Loop HW Supply Outlet; !- Name of the set point
Node
> >
> > Note, I am using the boiler simple object. Thanks in advance.
> >
> > Noel
> >
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf
under the
> > Documentation link and press the "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@...
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/