No.  Higher chilled water supply temperatures should reduce chiller power 
consumption for the same load.  This assumes that the chiller EIR as a function 
of temperature curve is valid.  One would also expect the load to fall because 
the latent cooling at the coils should fall with higher water temperatures.

Mike


On 5 Jun 2007 at 22:26, noelcrrl wrote:

> Hi Mike...thanks for the response...
> 
> I am having the same issue with chilled water reset...is this to be 
> expected?
> 
> Noel
> 
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" 
> <mjwitte@...> wrote:
> >
> > No, BOILER:SIMPLE does nothing more than apply the nominal 
> efficiency and a 
> > part-load curve.  It does not model any jacket losses, and so it's 
> efficiency 
> > is not sensitive to the supply temperature.  Also, with no piping 
> losses in the 
> > simulation, that effect is not present either.  So, I would expect 
> the same 
> > boiler energy consumption for these two cases.
> > 
> > I can't think of an easy way to model this with current 
> capabilities.
> > 
> > Mike
> > 
> > 
> > On 1 Jun 2007 at 2:44, noelcrrl wrote:
> > 
> > > Dear All-
> > > 
> > > I am tying to estimate the energy savings of implementing a hot 
> water 
> > > reset as a function of outside air.  The object was entered as 
> shown 
> > > at the end of this message.  When I implement the hot water 
> reset, 
> > > the energy consumption of the boiler does not change-no energy 
> > > savings.  Why is this the case?  Does the boiler:simple object 
> take 
> > > into account water delivery temperature into its energy 
> consumption 
> > > calculation?
> > > 
> > > SET POINT MANAGER:OUTSIDE AIR,
> > >     Hot Water Loop HW Temp Manager,  !- Name
> > >     TEMP,                    !- Control variable
> > >     82.2,                    !- Set point at outside low {C}
> > >     -6.7,                    !- Outside low {C}
> > >     65.6,                    !- Set point at outside high {C}
> > >     10,                      !- Outside high {C}
> > >     Hot Water Loop HW Supply Outlet;  !- Name of the set point 
> Node 
> > > 
> > > Note, I am using the boiler simple object.  Thanks in advance.
> > > 
> > > Noel
> > > 
> > > 
> > > 
> > > 
> > > 
> > > 
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > > 
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > 
> > > Attachments are not allowed -- please post any files to the 
> appropriate folder
> > > in the Files area of the Support Web Site.
> > > 
> > > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf 
> under the
> > > Documentation link and press the "search" button.
> > > 
> > > Yahoo! Groups Links
> > > 
> > > 
> > > 
> > > 
> > > 
> > 
> > 
> > ========================================================
> > Michael J. Witte, GARD Analytics, Inc.
> > EnergyPlus Testing and Support      
> > EnergyPlus-Support@...
> >
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/