RE: [EnergyPlus_Support] Re: Wall condensation



If you want to alter the modeling when evaluating condensation, EnergyPlus lets you set the values for convection coefficients (as well as 3-d radiation view factors).  Another useful strategy is to break up surfaces into different parts and set up a portion of them to represent the thermal bridges. 

 

I guess you are referring here to the one-dimensional analysis of transient conduction heat transfer within a surface, but readers should note that interactions between the surface and other building elements *are* included in the zone heat balance model and these are modeled in multiple dimensions (it is a goal).  In my opinion, EnergyPlus's zone heat balance model does a fairly good job of calculating surface temperatures.  It includes long-wave radiation exchange with the other surfaces in the room and short wave energy from solar and lights.  

 

I would agree with you that it is possible to do better calculations of localized condensation at a single point using multidimensional tools (e.g. FEA, conjugate-CFD).  Such tools might be good for research, product design, or performance ratings, but I doubt they are useful for analyzing an entire building over the course of a year's worth of weather.  

 

 

________________________________

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of josep.sole@xxxxxxxxxxx
Sent: Thursday, June 07, 2007 8:30 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: RE: [EnergyPlus_Support] Re: Wall condensation

 

I'm not sure if these variables are absolutely correctly calculated.

Point temperature (for condensation purpose) it's always a bi dimensional o three-dimensional o forth dimensional problem in my opinion interactions between adjacent building components are not well modelisated in Energy plus (it's not the goal!).

Usually condensation analysis needs different film coefficients factors than energetic calculation.

Josep Sole 
URSA Iberica Aislantes SA 
www.ursa.es <http://www.ursa.es <http://www.ursa.es> > 

________________________________

De: EnergyPlus_Support@xxxxxxxxxxxxxxx <mailto:EnergyPlus_Support%40yahoogroups.com>  [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx <mailto:EnergyPlus_Support%40yahoogroups.com> ] En nombre de Michael J. Witte
Enviado el: jueves, 07 de junio de 2007 0:13
Para: EnergyPlus_Support@xxxxxxxxxxxxxxx <mailto:EnergyPlus_Support%40yahoogroups.com> 
Asunto: Re: [EnergyPlus_Support] Re: Wall condensation

There are report variables for window surfaces only:

Zone,Average,Inside Glass Condensation Flag[]
Zone,Average,Inside Frame Condensation Flag[]
Zone,Average,Inside Divider Condensation Flag[]

Mike

On 6 Jun 2007 at 21:54, Miguel Angel Pascual wrote:

> Thanks for your answer. I have been looking for the report variable for the
> condensation flag but I could't find it. Is it something direct or do we have to
> postprocess the surface and dew point temperatures?
> 
> Thanks. 
> 
> 
> 
> ---
> Miguel Angel Pascual Buisan
> 
> 
> -----Original Message-----
> From: "Michael J. Witte" <mjwitte@xxxxxxxx <mailto:mjwitte%40gard.com>  <mailto:mjwitte%40gard.com> >
> Date: Wed, 06 Jun 2007 16:30:27 
> To:EnergyPlus_Support@xxxxxxxxxxxxxxx <mailto:EnergyPlus_Support%40yahoogroups.com>  <mailto:EnergyPlus_Support%40yahoogroups.com> 
> Subject: Re: [EnergyPlus_Support] Re: Wall condensation
> 
> EnergyPlus does not model condensation on windows or wall surfaces. EnergyPlus 
> only reports if condensation would occur (simply by comparing the surface
> temperature with the zone dew point).
> 
> Mike
> 
> On 2 Jun 2007 at 3:20, ooikoonbeng2004 wrote:
> 
> > My simulation using schedules that turns on the airconditioner and 
> > then off it, the temparature on the window glass dips in the next 
> > hour after the aircond is turned off. i am not sure whether this is 
> > the condensation on the glass. i do not recall seeing this in the 
> > documentation. 
> > ooi 
> > --- In EnergyPlus_Support@: <mailto:EnergyPlus_Support%40yahoogroups.com>
> yahoogroups.com, "Miguel Angel Pascual" > <mapascual@...> wrote: > > > > Hello:
> > > > > > > > > I would like to know if energyplus can report wall condensation
> in > the > > inside face of the walls. > > > > > > > > Thanks in advance. > > >
> > > > > > Miguel Ángel Pascual > > > > Director Técnico > > > > > > > > MIYABI
> espacios urbanos bioclimáticos > > > > Leyre 11bis, 1ºC 31002 Pamplona > > > >
> Tel: 948 20 36 44 Fax: 948 20 78 60 > > > > Email: mapascual@... > > > > Web:
> <http://www.miyabi.: <http://www.miyabi.:>  <http://www.miyabi.: <http://www.miyabi.:> > <http://www.miyabi.es/ <http://www.miyabi.es/>  <http://www.miyabi.es/ <http://www.miyabi.es/> > > es/> www.miyabi.es > > > > > > > >
> > > > > > > > > [Non-text portions of this message have been removed] > > > > >
> > > The primary EnergyPlus web site is found at: > http://www.energypl: <http://www.energypl:>  <http://www.energypl: <http://www.energypl:> > 
> <http://www.energyplus.gov <http://www.energyplus.gov>  <http://www.energyplus.gov <http://www.energyplus.gov> > > us.gov > > The group web site is: > http://groups.: <http://groups.:>  <http://groups.: <http://groups.:> > 
> <http://groups.yahoo.com/group/EnergyPlus_Support/ <http://groups.yahoo.com/group/EnergyPlus_Support/>  <http://groups.yahoo.com/group/EnergyPlus_Support/ <http://groups.yahoo.com/group/EnergyPlus_Support/> > >
> yahoo.com/group/EnergyPlus_Support/ > > Attachments are not allowed -- please
> post any files to the appropriate folder > in the Files area of the Support Web
> Site. > > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under
> the > Documentation link and press the "search" button. > > Yahoo! Groups Links
> > > > > > 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support 
> EnergyPlus-Support@: <mailto:EnergyPlus-Support%40gard.com> gard.com
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov <http://www.energyplus.gov>  <http://www.energyplus.gov <http://www.energyplus.gov> > 
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/ <http://groups.yahoo.com/group/EnergyPlus_Support/>  <http://groups.yahoo.com/group/EnergyPlus_Support/ <http://groups.yahoo.com/group/EnergyPlus_Support/> > 
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 

[Non-text portions of this message have been removed]

 



[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/