Please provide more information about the input data file you are 
looking at.  If its one of the example files distributed with 
EnergyPlus, please specify which file.

Each chiller will have an output report variable for its "Chiller 
Electric Power [W]" and its "Chiller Electric Consumption [J]" (see IO 
Reference, section "Generic Chiller Outputs" and section "Report 
Variable").  You should sum the values for each chiller if you want to 
know the total electric power or electric consumption for the two 
chillers.  As an alternative, the "Chiller Electric Consumption [J]" is 
metered (i.e., summed for all electric chillers) on Electricity:Plant 
... however, this meter will also contain the pump energy and cooling 
tower fan energy if a tower is being simulated.  Look in the IO 
Reference at the section entitled "Report Meter, Report MeterFile Only" 
for more information regarding report meters.

Without knowing the specifics about the input file you are looking at, 
it is hard to answer your question about the "difference of two chillers 
and their work".  Assuming this is one of the EnergyPlus example files, 
I suspect that the file is simply showing how multiple chillers can be 
specified for a chiller plant and that their time-of-day operation can 
be scheduled by the user.


love9787m wrote:

>Hi,
>
>In plant equpment, the simulation model contains two chiller, big 
>chiller and littlet chiller. 
>Generally, Big chiller operates from morning to noon time and adversely 
>little chiller operates from afternoon to night.   
>By the way, When calculatting the energy consumption to the chiller 
>electricity, should I sum those two values?
>Please provide me with the information between two chillers, 
>I'm not sure about difference of two chillers and their work.
>Thank you in advance
>  
>


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/