In the current release of EnergyPlus, you can only use DX cooling coil in the 
outside air system.  There is no example file for this.  Add a DXSYSTEM:AIRLOOP 
object to the equipment list for the outside air system and connect the nodes 
as appropriate.  Then add a DX coil object as a child of the DXSYSTEM:AIRLOOP.

Mike


On 26 Jun 2007 at 6:49, love9787m wrote:

> Hi, 
> Currently, modeling the cooling system based on desiccant control.
> So I want know energy consumption and indoor envirnoment.
> There are several configurations of system based on component location.
> First, desiccant wheel upstream of cooling coil.
> Second, desiccant wheel downstream of cooling coil.
> The shift of cooling coil will make different results as expected.
> So location of cooling coil is the most considerable variable.
> Generally, In Air loop Main branch object input, 
> Comp1:Outsidea Air System
> Comp2:Supply fan
> Comp3:main coolingcoil 
> as sequence.
> But I want to move main coolingcoil into the Outside Air System.
> In the Outside Air System, I want to make Ousdie Air system like this 
> first desiccant wheel andthen cooling coil andthen heat recovery.
> This is a Outside Air system configuraton in the Air loop branch
> I imaged, 
> So please let me the way to change the locatio of coolingcoil or 
> provide ex,idf file to me.
> Thank you in advance. 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/