Re: [EnergyPlus_Support] Terminal equipment don't work
There are many possible reasons:
1. Thermostat type must be SINGLE HEATING COOLING SETPOINT or DUAL SETPOINT
WITH DEADBAND.
2. Are the reheat coils scheduled on?
3. Are the reheat coils large enough?
4. If the reheat coils are hot water, is the hot water loop active? Boiler
large enough?
Compare your model with the TermReheat.idf example file to see you have similar
kinds of control components.
Mike
On 10 Jul 2007 at 9:34, hbn_pch wrote:
> Hi,i make a model with terminal reheat system.The terminal equipment is
> single duct :const volume:reheat.
> The temperature control setpoint in summer is 25C and the humidity
> control setpoint is 60.After simulating,
> i found that the humidity is around setpoint,but the temperature is
> lower than setpoint(around 20C).I check
> the output file and found the terminal equipment do not work at all.
> (sometimes only several terminal equipment
> work and then such zones will achieve temperature setpoint).I think,now
> that the supply air temperature is overcold
> ,the terminal equipment should work to reheat the air to setpoint.I'm
> puzzled.
>
> Can anybody tell me what factors would effect the terminal equipment
> working?
>
> Appreciated your kind help.Thanks
>
> pch
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/