Re: [EnergyPlus_Support] Sensible cooling energy and sensible cooling rate is empty
Empty cells mean there is a schedule on the REPORT VARIABLE object that is
turnning off reporting during these times. First, get rid of the schedules so
you can see all of the data.
There a many possible reasons that the building might not maintain control at
peak hours - airflow too small, coil too small, chiller too small, bad
controls, etc. You will need to report enough information to see if the
equipment is operating and if the supply water and air temperature setpoints
are being maintained.
Mike
On 1 Aug 2007 at 17:15, love9787m wrote:
> Hi
> Currently running the simulation on two zones.
> First separate two zone from one single zone which is center zone and
> outside zone.
> Center zone is served by VAVsystem and outside zone is served by PTHT.
> In the output file, sensible cooling energy and rate is empty in
> outside zone(PTHP Zone) from 2 PM to 6 PM normally and this term is
> varied according to the weather condition.
> Normally, Snesible cooling energy and rate is empty during the peak
> load time.
> At a result, indoor air temperature is higher and PMV is higher as well.
> What is the problem on this sensible cooling operation.
> Please help.
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/