Re: [EnergyPlus_Support] Re: Primary-Secondary System zero flow issue
EnergyPlus 2.0.0.025 can autosize a primary-secondary system when using the
COMMON PIPE option with a single PLANT LOOP object. See example file
CommonPipe_Pri-Sec.idf
5zoneVAV-Pri-SecLoop.idf still uses the older CONNECTION
COMPONENT:PLANTLOOP:CONTROLLED approach which uses two complete PLANT LOOP
structures to accomplish primary-secondary. When using that approach,
autosizing does not work for the primary loop.
Mike
On 13 Aug 2007 at 18:25, fernandowestphal wrote:
> Dear All,
>
> Any news about this subject?
> Is the actual version of E+ (2.0.0.025) doing the autosize for the
> primary side of primary-secondary systems?
>
> I've tried to do it in the example file "5zoneVAV-Pri-SecLoop.idf"
> and I got chiller with zero capacity and zero flows in the primary
> loop...
>
> Thanks!
> Fernando Simon Westphal
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
> <mjwitte@...> wrote:
> >
> > Autosizing does not currently work for the primary loop in a
> primary-secondary
> > system. In the next release (April 2007), primary-secondary
> systems will be
> > able to be modeled using a single PLANT LOOP with no connection
> component.
> > Autosizing will then flow through to the primary side. Until then,
> you must
> > specify the primary equipment capacities and flow rates.
> >
> > Mike
> >
> >
> > On 16 Jan 2007 at 3:19, miaoworld wrote:
> >
> > > Greetings,
> > >
> > > I have a primary and secondary chilled water system, and I am
> keeping
> > > having zero flow. I have specified the primary pump consumption
> and
> > > flow rate for the primary chilled water loop, but the primary
> loop and
> > > condenser loop (Autosized) is zero flow.
> > >
> > > Any suggestions will be appreciated.
> > >
> > > Thanks.
> > >
> > > Miao(Eric)
> > >
> > > ************* Beginning System Sizing Calculations
> > > ** Warning ** SizeCondDemandSide: Calculated Plant Sizing
> Design
> > > Volume Flow Rate=[0.00] is too small. Set to 0.0
> > > ** ~~~ ** ..occurs for Condenser Loop=CHILLED WATER LOOP
> > > CONDENSER WATER LOOP
> > > ** Warning ** SizeCondSupplySide: Calculated Plant Sizing
> Design
> > > Volume Flow Rate=[0.00] is too small. Set to 0.0
> > > ** ~~~ ** ..occurs for Condenser Loop=CHILLED WATER LOOP
> > > CONDENSER WATER LOOP
> > > ** Warning ** SizePump: Calculated Pump Nominal Volume Flow
> > > Rate=[0.00] is too small. Set to 0.0
> > > ** ~~~ ** ..occurs for Pump=CHILLED WATER LOOP CNDW SUPPLY
> PUMP
> > >
> > >
> > > ******Component sizing
> > >
> > > Component Sizing, CHILLER:ELECTRIC:EIR, CHILLER, Reference
> Evaporator
> > > Volumetric Water Flow Rate [m3/s], 0.0000
> > > Component Sizing, CHILLER:ELECTRIC:EIR, CHILLER, Reference
> Capacity
> > > [W], 0.0000
> > > Component Sizing, CHILLER:ELECTRIC:EIR, CHILLER, Reference
> Condenser
> > > Volumetric Water Flow Rate [m3/s], 0.0000
> > > Component Sizing, PUMP:CONSTANT SPEED, HOT WATER LOOP HW SUPPLY
> PUMP,
> > > Rated Volumetric Flow Rate [m3/s], 0.55510E-01
> > > Component Sizing, PUMP:CONSTANT SPEED, HOT WATER LOOP HW SUPPLY
> PUMP,
> > > Rated Power Consumption [W], 14182.
> > > Component Sizing, PUMP:VARIABLE SPEED, CHILLED WATER LOOP CHW SEC
> > > SUPPLY PUMP, Rated Power Consumption [W], 158.35
> > > Component Sizing, CONDENSER LOOP, CHILLED WATER LOOP CONDENSER
> WATER
> > > LOOP, Volume of the condenser loop [m3], 0.0000
> > > Component Sizing, CONDENSER LOOP, CHILLED WATER LOOP CONDENSER
> WATER
> > > LOOP, Maximum Loop Volumetric Flow Rate [m3/s], 0.0000
> > > Component Sizing, COOLING TOWER:SINGLE SPEED, MAIN TOWER,
> Autosized
> > > design water flow rate [m3/s], 0.0000
> > > Component Sizing, COOLING TOWER:SINGLE SPEED, MAIN TOWER, Fan
> power
> > > at design air flow rate [W], 0.0000
> > > Component Sizing, COOLING TOWER:SINGLE SPEED, MAIN TOWER, Design
> air
> > > flow rate [m3/s], 0.0000
> > > Component Sizing, COOLING TOWER:SINGLE SPEED, MAIN TOWER,
> Autosized
> > > tower UA value at the design air flow rate [W/C], 0.0000
> > > Component Sizing, COOLING TOWER:SINGLE SPEED, MAIN TOWER, Air
> flow
> > > rate in free convection regime [m3/s], 0.0000
> > > Component Sizing, COOLING TOWER:SINGLE SPEED, MAIN TOWER, Tower
> UA
> > > value in free convection regime [W/C], 0.0000
> > > Component Sizing, PUMP:VARIABLE SPEED, CHILLED WATER LOOP CNDW
> SUPPLY
> > > PUMP, Rated Volumetric Flow Rate [m3/s], 0.0000
> > > Component Sizing, PUMP:VARIABLE SPEED, CHILLED WATER LOOP CNDW
> SUPPLY
> > > PUMP, Rated Power Consumption [W], 0.0000
> > >
> > >
> > >
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > >
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > > Attachments are not allowed -- please post any files to the
> appropriate folder in the Files area of the Support Web Site.
> > >
> > > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
> and press the "search" button.
> > >
> > > Yahoo! Groups Links
> > >
> > >
> > >
> > >
> > >
> >
> >
> > ========================================================
> > Michael J. Witte, GARD Analytics, Inc.
> > EnergyPlus Testing and Support
> > EnergyPlus-Support@...
> >
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/