[EnergyPlus_Support] Node Connection Errors



Hello!

These are the idf and error file.

Can you help me?!?!

idf file:

http://www.cgrafica.helloweb.eu/home/download.php?list.8

Error file:

Program Version,EnergyPlus 2.0.0.025, 01/09/2007 13.57,IDD_Version 2.0.0.025
   ************* Beginning Zone Sizing Calculations
   ** Warning ** DXFOut: Could not triangulate surface="W_43592_2_0_1", type="Wall", 
check surface vertex order(entry)
   ** Warning ** DXFOut: Could not triangulate surface="W_43592_2_0_2", type="Wall", 
check surface vertex order(entry)
   ** Warning ** DXFOut: Could not triangulate surface="W_43631_6_0_1", type="Wall", 
check surface vertex order(entry)
   ** Warning ** DXFOut: Could not triangulate surface="W_43154_6_0_1", type="Wall", 
check surface vertex order(entry)
   ** Warning ** DXFOut: Could not triangulate surface="S_43469_0_0_0", type="Floor", 
check surface vertex order(entry)
   ** Warning ** DXFOut: Could not triangulate surface="C_43469_10016_0_10017", 
type="Roof", check surface vertex order(entry)
   ** Warning ** DXFOut: Could not triangulate surface="R_43469_1_5_0", type="Roof", 
check surface vertex order(entry)
   ** Warning ** Inside surface heat balance did not converge with Max Temp Difference [C] 
=4.882E-003 vs Max Allowed Temp Diff [C] =2.000E-003
   **   ~~~   **  Occurrence info=WINTER DESIGN DAY IN EINSTEIN LORETO, 01/15 09:00 - 
10:00
   ** Warning ** Inside surface heat balance did not converge with Max Temp Difference [C] 
=6.555E-003 vs Max Allowed Temp Diff [C] =2.000E-003
   **   ~~~   **  Occurrence info=WINTER DESIGN DAY IN EINSTEIN LORETO, 01/15 10:00 - 
10:01
   ** Warning ** Inside surface heat balance did not converge with Max Temp Difference [C] 
=4.576E-003 vs Max Allowed Temp Diff [C] =2.000E-003
   **   ~~~   **  Occurrence info=WINTER DESIGN DAY IN EINSTEIN LORETO, 01/15 11:00 - 
11:15
   ** Warning ** Inside surface heat balance did not converge with Max Temp Difference [C] 
=4.020E-003 vs Max Allowed Temp Diff [C] =2.000E-003
   **   ~~~   **  Occurrence info=WINTER DESIGN DAY IN EINSTEIN LORETO, 01/15 12:00 - 
12:02
   ** Warning ** Inside surface heat balance did not converge with Max Temp Difference [C] 
=3.038E-003 vs Max Allowed Temp Diff [C] =2.000E-003
   **   ~~~   **  Occurrence info=WINTER DESIGN DAY IN EINSTEIN LORETO, 01/15 13:00 - 
13:04
   ** Warning ** Inside surface heat balance did not converge with Max Temp Difference [C] 
=3.782E-003 vs Max Allowed Temp Diff [C] =2.000E-003
   **   ~~~   **  Occurrence info=WINTER DESIGN DAY IN EINSTEIN LORETO, 01/15 15:00 - 
15:02
   ** Warning ** Inside surface heat balance did not converge with Max Temp Difference [C] 
=4.220E-003 vs Max Allowed Temp Diff [C] =2.000E-003
   **   ~~~   **  Occurrence info=WINTER DESIGN DAY IN EINSTEIN LORETO, 01/15 16:00 - 
16:04
   ** Warning ** Inside surface heat balance did not converge with Max Temp Difference [C] 
=4.024E-003 vs Max Allowed Temp Diff [C] =2.000E-003
   **   ~~~   **  Occurrence info=WINTER DESIGN DAY IN EINSTEIN LORETO, 01/15 17:00 - 
17:04
   ** Warning ** Inside surface heat balance did not converge with Max Temp Difference [C] 
=2.824E-003 vs Max Allowed Temp Diff [C] =2.000E-003
   **   ~~~   **  Occurrence info=WINTER DESIGN DAY IN EINSTEIN LORETO, 01/15 18:00 - 
19:00
   ** Warning ** Inside surface heat balance did not converge with Max Temp Difference [C] 
=2.042E-003 vs Max Allowed Temp Diff [C] =2.000E-003
   **   ~~~   **  Occurrence info=WINTER DESIGN DAY IN EINSTEIN LORETO, 01/15 19:00 - 
20:00
   ** Warning ** Calculated design heating load for zone=43592 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43624 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43631 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43657 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43666 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43673 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43680 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43687 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43694 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43701 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43708 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43723 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43739 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43746 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43753 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43760 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43767 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43775 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43782 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43789 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43154 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43180 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43189 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43196 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43203 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43210 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43217 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43224 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43231 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43238 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43247 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43256 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43276 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43295 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43304 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43311 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43318 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43325 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43332 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43339 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43346 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43353 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43362 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43371 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43269 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43460 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43469 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43501 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43508 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43515 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43522 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43529 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43536 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43543 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43550 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43558 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43565 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43575 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated design heating load for zone=43584 is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ************* Beginning System Sizing Calculations
   ** Warning ** Calculated heating design air flow rate for system=43592 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43624 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43631 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43657 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43666 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43673 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43680 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43687 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43694 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43701 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43708 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43723 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43739 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43746 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43753 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43760 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43767 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43775 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43782 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43789 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43154 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43180 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43189 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43196 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43203 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43210 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43217 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43224 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43231 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43238 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43247 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43256 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43276 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43295 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43304 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43311 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43318 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43325 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43332 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43339 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43346 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43353 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43362 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43371 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43269 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43460 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43469 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43501 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43508 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43515 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43522 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43529 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43536 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43543 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43550 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43558 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43565 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43575 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Warning ** Calculated heating design air flow rate for system=43584 AHU is zero.
   **   ~~~   ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
   ** Severe  ** Air Primary Loop 43501 AHU has no air flow
   **   ~~~   ** Check flow rate inputs for components in this air loop and,
   **   ~~~   ** if autosized, check ZONE SIZING and SYSTEM SIZING and related inputs.
   **  Fatal  ** Previous condition causes termination.
   ************* Fatal error -- final processing.  More error messages may appear.
   ************* Testing Individual Branch Integrity
   ************* All Branches passed integrity testing
   ************* Testing Individual Supply Air Path Integrity
   ************* All Supply Air Paths passed integrity testing
   ************* Testing Individual Return Air Path Integrity
   ************* All Return Air Paths passed integrity testing
   ** Severe  ** Node Connection Error, Node="43592 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43592 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43624 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43624 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43631 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43631 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43657 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43657 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43666 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43666 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43673 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43673 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43680 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43680 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43687 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43687 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43694 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43694 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43701 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43701 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43708 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43708 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43723 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43723 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43739 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43739 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43746 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43746 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43753 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43753 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43760 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43760 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43767 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43767 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43775 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43775 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43782 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43782 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43789 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43789 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43154 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43154 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43180 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43180 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43189 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43189 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43196 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43196 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43203 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43203 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43210 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43210 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43217 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43217 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43224 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43224 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43231 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43231 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43238 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43238 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43247 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43247 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43256 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43256 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43276 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43276 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43295 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43295 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43304 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43304 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43311 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43311 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43318 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43318 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43325 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43325 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43332 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43332 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43339 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43339 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43346 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43346 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43353 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43353 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43362 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43362 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43371 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43371 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43269 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43269 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43460 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43460 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43469 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43469 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43501 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43501 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43508 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43508 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43515 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43515 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43522 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43522 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43529 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43529 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43536 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43536 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43543 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43543 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43550 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43550 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43558 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43558 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43565 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43565 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43575 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43575 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Severe  ** Node Connection Error, Node="43584 AHU SUPPLY FAN OUTLET", Sensor 
node did not find a matching node of appropriate type (Actuator, Sensor, OutsideAir).
   **   ~~~   ** Reference Object=SET POINT MANAGER:MIXED AIR, Name=43584 AHU 
COOLING COIL AIR TEMP MANAGER
   ** Warning ** Node Connection errors shown during "fatal error" processing may be false 
because not all inputs may have been retrieved.
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43592 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43592 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43592 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43624 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43624 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43624 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43631 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43631 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43631 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43657 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43657 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43657 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43666 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43666 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43666 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43673 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43673 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43673 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43680 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43680 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43680 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43687 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43687 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43687 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43694 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43694 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43694 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43701 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43701 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43701 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43708 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43708 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43708 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43723 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43723 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43723 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43739 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43739 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43739 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43746 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43746 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43746 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43753 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43753 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43753 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43760 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43760 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43760 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43767 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43767 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43767 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43775 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43775 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43775 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43782 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43782 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43782 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43789 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43789 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43789 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43154 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43154 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43154 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43180 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43180 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43180 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43189 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43189 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43189 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43196 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43196 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43196 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43203 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43203 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43203 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43210 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43210 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43210 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43217 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43217 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43217 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43224 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43224 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43224 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43231 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43231 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43231 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43238 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43238 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43238 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43247 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43247 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43247 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43256 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43256 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43256 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43276 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43276 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43276 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43295 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43295 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43295 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43304 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43304 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43304 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43311 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43311 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43311 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43318 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43318 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43318 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43325 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43325 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43325 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43332 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43332 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43332 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43339 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43339 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43339 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43346 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43346 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43346 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43353 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43353 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43353 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43362 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43362 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43362 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43371 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43371 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43371 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43269 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43269 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43269 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43460 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43460 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43460 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43469 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43469 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43469 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43501 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43501 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43501 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43508 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43508 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43508 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43515 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43515 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43515 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43522 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43522 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43522 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43529 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43529 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43529 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43536 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43536 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43536 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43543 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43543 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43543 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43550 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43550 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43550 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43558 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43558 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43558 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43565 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43565 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43565 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43575 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43575 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43575 AHU AIR LOOP OUTLET
   ** Warning ** Potential Node Connection Error for object FURNACE:HEATCOOL, 
name=43584 AHU FURNACE WITH DX COOLING
   **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further 
information
   **   ~~~   **   Inlet Node : 43584 AHU MIXED AIR OUTLET
   **   ~~~   **   Outlet Node: 43584 AHU AIR LOOP OUTLET
   ************* There were 118 node connection errors noted.
   *************
   ************* ===== Final Error Summary =====
   ************* The following error categories occurred.  Consider correcting or noting.
   ************* Node Connection Errors
   ************* ..Node connection errors are often caused by spelling mistakes in a node 
name field.
   ************* ..To track down the problem, search the idf file for each node name listed 
to see if it
   ************* ..occurs in the expected input fields.
   *************
   ************* EnergyPlus Terminated--Fatal Error Detected. 195 Warning; 60 Severe 
Errors; Elapsed Time=00hr 03min  7.50sec



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/