Re: [EnergyPlus_Support] Re: Primary-Secondary System zero flow issue
This configuration should be supported in this version. Please upload your
input file to the yahoo group files area or send as a zipped attachment to
energyplus-support@xxxxxxxx
Mike
On 3 Sep 2007 at 15:08, fernandowestphal wrote:
> Hi, Mike.
>
> I've tried the COMMON PIPE option to simulate a primary-secondary
> system, but now I got this message:
>
> ** Severe ** Current version does not support Loop pumps and branch
> pumps together
> ** ~~~ ** Occurs in loop CHILLED WATER LOOP
>
> I am trying to modelate a primary-secondary loop system, as specified
> by ASHRAE Std 90.1 AppG - system 8, with branch pumps on supply side
> (one pump for each chiller; with 3 chillers) and a loop pump in the
> demand side (a variable flow pump for the cooling coils - secondary
> loop).
>
> According to this severe error message I suppose that the current
> version of E+ does not support such a configuration.
> Am I right, or I am missing something?
> Any suggestion to modelate such a structure?
>
> Best regards,
> Fernando Westphal
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
> <mjwitte@...> wrote:
> >
> > EnergyPlus 2.0.0.025 can autosize a primary-secondary system when
> using the
> > COMMON PIPE option with a single PLANT LOOP object. See example
> file
> > CommonPipe_Pri-Sec.idf
> >
> > 5zoneVAV-Pri-SecLoop.idf still uses the older CONNECTION
> > COMPONENT:PLANTLOOP:CONTROLLED approach which uses two complete
> PLANT LOOP
> > structures to accomplish primary-secondary. When using that
> approach,
> > autosizing does not work for the primary loop.
> >
> > Mike
> >
> >
> > On 13 Aug 2007 at 18:25, fernandowestphal wrote:
> >
> > > Dear All,
> > >
> > > Any news about this subject?
> > > Is the actual version of E+ (2.0.0.025) doing the autosize for
> the
> > > primary side of primary-secondary systems?
> > >
> > > I've tried to do it in the example file "5zoneVAV-Pri-
> SecLoop.idf"
> > > and I got chiller with zero capacity and zero flows in the
> primary
> > > loop...
> > >
> > > Thanks!
> > > Fernando Simon Westphal
> > >
> > >
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
> > > <mjwitte@> wrote:
> > > >
> > > > Autosizing does not currently work for the primary loop in a
> > > primary-secondary
> > > > system. In the next release (April 2007), primary-secondary
> > > systems will be
> > > > able to be modeled using a single PLANT LOOP with no connection
> > > component.
> > > > Autosizing will then flow through to the primary side. Until
> then,
> > > you must
> > > > specify the primary equipment capacities and flow rates.
> > > >
> > > > Mike
> > > >
> > > >
> > > > On 16 Jan 2007 at 3:19, miaoworld wrote:
> > > >
> > > > > Greetings,
> > > > >
> > > > > I have a primary and secondary chilled water system, and I am
> > > keeping
> > > > > having zero flow. I have specified the primary pump
> consumption
> > > and
> > > > > flow rate for the primary chilled water loop, but the primary
> > > loop and
> > > > > condenser loop (Autosized) is zero flow.
> > > > >
> > > > > Any suggestions will be appreciated.
> > > > >
> > > > > Thanks.
> > > > >
> > > > > Miao(Eric)
> > > > >
> > > > > ************* Beginning System Sizing Calculations
> > > > > ** Warning ** SizeCondDemandSide: Calculated Plant Sizing
> > > Design
> > > > > Volume Flow Rate=[0.00] is too small. Set to 0.0
> > > > > ** ~~~ ** ..occurs for Condenser Loop=CHILLED WATER
> LOOP
> > > > > CONDENSER WATER LOOP
> > > > > ** Warning ** SizeCondSupplySide: Calculated Plant Sizing
> > > Design
> > > > > Volume Flow Rate=[0.00] is too small. Set to 0.0
> > > > > ** ~~~ ** ..occurs for Condenser Loop=CHILLED WATER
> LOOP
> > > > > CONDENSER WATER LOOP
> > > > > ** Warning ** SizePump: Calculated Pump Nominal Volume Flow
> > > > > Rate=[0.00] is too small. Set to 0.0
> > > > > ** ~~~ ** ..occurs for Pump=CHILLED WATER LOOP CNDW
> SUPPLY
> > > PUMP
> > > > >
> > > > >
> > > > > ******Component sizing
> > > > >
> > > > > Component Sizing, CHILLER:ELECTRIC:EIR, CHILLER, Reference
> > > Evaporator
> > > > > Volumetric Water Flow Rate [m3/s], 0.0000
> > > > > Component Sizing, CHILLER:ELECTRIC:EIR, CHILLER, Reference
> > > Capacity
> > > > > [W], 0.0000
> > > > > Component Sizing, CHILLER:ELECTRIC:EIR, CHILLER, Reference
> > > Condenser
> > > > > Volumetric Water Flow Rate [m3/s], 0.0000
> > > > > Component Sizing, PUMP:CONSTANT SPEED, HOT WATER LOOP HW
> SUPPLY
> > > PUMP,
> > > > > Rated Volumetric Flow Rate [m3/s], 0.55510E-01
> > > > > Component Sizing, PUMP:CONSTANT SPEED, HOT WATER LOOP HW
> SUPPLY
> > > PUMP,
> > > > > Rated Power Consumption [W], 14182.
> > > > > Component Sizing, PUMP:VARIABLE SPEED, CHILLED WATER LOOP
> CHW SEC
> > > > > SUPPLY PUMP, Rated Power Consumption [W], 158.35
> > > > > Component Sizing, CONDENSER LOOP, CHILLED WATER LOOP
> CONDENSER
> > > WATER
> > > > > LOOP, Volume of the condenser loop [m3], 0.0000
> > > > > Component Sizing, CONDENSER LOOP, CHILLED WATER LOOP
> CONDENSER
> > > WATER
> > > > > LOOP, Maximum Loop Volumetric Flow Rate [m3/s], 0.0000
> > > > > Component Sizing, COOLING TOWER:SINGLE SPEED, MAIN TOWER,
> > > Autosized
> > > > > design water flow rate [m3/s], 0.0000
> > > > > Component Sizing, COOLING TOWER:SINGLE SPEED, MAIN TOWER,
> Fan
> > > power
> > > > > at design air flow rate [W], 0.0000
> > > > > Component Sizing, COOLING TOWER:SINGLE SPEED, MAIN TOWER,
> Design
> > > air
> > > > > flow rate [m3/s], 0.0000
> > > > > Component Sizing, COOLING TOWER:SINGLE SPEED, MAIN TOWER,
> > > Autosized
> > > > > tower UA value at the design air flow rate [W/C], 0.0000
> > > > > Component Sizing, COOLING TOWER:SINGLE SPEED, MAIN TOWER,
> Air
> > > flow
> > > > > rate in free convection regime [m3/s], 0.0000
> > > > > Component Sizing, COOLING TOWER:SINGLE SPEED, MAIN TOWER,
> Tower
> > > UA
> > > > > value in free convection regime [W/C], 0.0000
> > > > > Component Sizing, PUMP:VARIABLE SPEED, CHILLED WATER LOOP
> CNDW
> > > SUPPLY
> > > > > PUMP, Rated Volumetric Flow Rate [m3/s], 0.0000
> > > > > Component Sizing, PUMP:VARIABLE SPEED, CHILLED WATER LOOP
> CNDW
> > > SUPPLY
> > > > > PUMP, Rated Power Consumption [W], 0.0000
> > > > >
> > > > >
> > > > >
> > > > > The primary EnergyPlus web site is found at:
> > > > > http://www.energyplus.gov
> > > > >
> > > > > The group web site is:
> > > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > > >
> > > > > Attachments are not allowed -- please post any files to the
> > > appropriate folder in the Files area of the Support Web Site.
> > > > >
> > > > > EnergyPlus Documentation is searchable. Open
> EPlusMainMenu.idf
> > > and press the "search" button.
> > > > >
> > > > > Yahoo! Groups Links
> > > > >
> > > > >
> > > > >
> > > > >
> > > > >
> > > >
> > > >
> > > > ========================================================
> > > > Michael J. Witte, GARD Analytics, Inc.
> > > > EnergyPlus Testing and Support
> > > > EnergyPlus-Support@
> > > >
> > >
> > >
> > >
> > >
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > >
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > > Attachments are not allowed -- please post any files to the
> appropriate folder
> > > in the Files area of the Support Web Site.
> > >
> > > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf
> under the
> > > Documentation link and press the "search" button.
> > >
> > > Yahoo! Groups Links
> > >
> > >
> > >
> > >
> > >
> >
> >
> > ========================================================
> > Michael J. Witte, GARD Analytics, Inc.
> > EnergyPlus Testing and Support
> > EnergyPlus-Support@...
> >
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/