RE: [EnergyPlus_Support] Fixed Minimum outside air rate



If I understand your system correctly, COMPACT HVAC:ZONE:FAN COIL would be 
equivalent - supply fan runs continously with fixed amount of outside air, hot 
water and chilled water coils modulate to meet the zone heating/cooling load.

If you prefer to keep what you have, change the SET POINT MANAGER:SCHEDULED 
objects for the heating and cooling coil to be SET POINT MANAGER:SINGLE ZONE 
HEATING and SET POINT MANAGER:SINGLE ZONE COOLING.  These will control the 
central coils based on the thermostat demand for a single zone.

Mike


On 22 Oct 2007 at 15:02, Aboye, Merid (US SSA) wrote:

> Mike,
> 
> 
> 
> In the actual system, heating and cooling supply temperatures are
> controlled, while flow rates are held constant. I used the COMPACT
> HVAC:SYSTEM:VAV object because the Compact HVAC feature does not offer
> the option to model constant-air flow rate systems with central boilers
> and air-cooled chillers.  What can I do to simulate a constant flow
> system without throwing out the expanded model? Thank you kindly for
> your support.
> 
> 
> 
> Merid 
> 
> 
> 
> ________________________________
> 
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Michael J.
> Witte
> Sent: Monday, October 22, 2007 2:36 PM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: RE: [EnergyPlus_Support] Fixed Minimum outside air rate
> 
> 
> 
> For this sytem type, in zone sizing, if the Min OA is greater than the
> cooling 
> supply flow rate, then the Min OA requirement will override. But it will
> not 
> check the min frac of a VAV terminal unit to make sure this is >= the
> Min OA 
> requirment for the zone. The only way to control this is to manually
> compute 
> the required min frac setting for the VAV terminal unit.
> 
> For the heating controls, I am still not completely sure what to
> recommend. 
> Will the heating mode supply air temperature be controlled to a fixed 
> temperature with all control made by varying the VAV damper? Or will the
> VAV 
> flow and supply temperature both vary?
> 
> The only option that will work directly from Compact HVAC is to delete
> the 
> central heating coil and add a hot water reheat coil with REVERSE ACTION
> 
> damper. This will give you the appropriate amount of heating energy, but
> it 
> might not give the correct amount of fan power, depending on the answer
> to my 
> question above.
> 
> Mike
> 
> On 15 Oct 2007 at 16:19, Aboye, Merid (US SSA) wrote:
> 
> > Mike,
> > 
> > 
> > 
> > Thank you for the reply.
> > 
> > 
> > 
> > Shortly after uploading the model last week, I changed the value of
> the
> > "Minimum Limit" field to "FIXED MINIMUM" in "CONTROLLER:OUTSIDE AIR"
> and
> > run the simulation. The change did not affect zones where the supply
> > flow rate is calculated to be less than the "FIXED MINIMUM" outside
> air
> > flow rate. In this case, the program simply reset the input "FIXED
> > MINIMUM" outside air rate to match the calculated design supply flow
> > rate. I am still not clear why that is occurring, but according to
> your
> > reply, it appears that I have bigger issues to resolve.
> > 
> > 
> > 
> > The system I am trying to model consists of (3) AHUs independently
> > serving (3) separate zones which have thermal interaction with one
> > another. Cooling and heating air is provided from each AHU to the zone
> > it serves, using a single-duct system. An air-cooled chiller and a
> > boiler supply cooling and heating coils within each AHU with 45oF CW
> and
> > 130 oF HW, respectively. The zone thermostat control is Dual Setpoint
> > with Deadband, which is a direct result of defining temperature
> > setpoints using the COMPACT:HVAC:THERMOSTAT object. Chiller Plant
> > Operating Scheme and Hot Water Plant Operating Scheme are both set to
> > the default type in their respective COMPACT:HVAC:PLANT objects.
> > 
> > 
> > 
> > Is there a COMPACT:HVAC object that I can define differently, such
> that
> > the expanded model will have coil controls that will be sensitive to
> > zone loads? Or, must the coil control scheme be defined in the
> Expanded
> > model? In any case, are there any sections of the User Guide or
> example
> > files you suggest I go over? 
> > 
> > 
> > 
> > Thank you for your valuable time.
> > 
> > 
> > 
> > Regards,
> > 
> > Merid 
> > 
> > 
> > 
> > ________________________________
> > 
> > From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> 
> > [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> ] On Behalf Of Michael J.
> > Witte
> > Sent: Monday, October 15, 2007 11:55 AM
> > To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> 
> > Subject: Re: [EnergyPlus_Support] Fixed Minimum outside air rate
> > 
> > 
> > 
> > On 10 Oct 2007 at 18:28, aboyemeplus wrote:
> > 
> > > I am running sizing simulations using winter and summer design-day 
> > > weather data. The minimum ventilation rate is set to a fixed value. 
> > > All other plant/system/zone level flow rates are auto sized. 
> > > While the results show the correct O/A rate for the summer design 
> > > day, winter O/A flow rates are much lower than the minimum fixed 
> > > rates entered in Zone/System sizing objects. 
> > 
> > In CONTROLLER:OUTSIDE AIR, the MinimumLimit field is set to
> > "PROPORTIONAL 
> > MINIMUM". This means the outside air amount will vary in proportion to
> > the 
> > total system air flow in this VAV system. If you want the OA quantity
> to
> > 
> > remain constant as the system flow varies, set this field to "FIXED
> > MINIMUM".
> > 
> > > The results also show that peak system heating and cooling
> capacities
> > > are comparable to values generated using a simpler model, one with
> > > "PURCHASED AIR" objects. However, the subject model depicts
> > > simultaneous heating and cooling during both design days, resulting
> in
> > > zone temperatures not meeting setpoint. Can anyone help me figure
> out
> > > 1)Why the minimum fixed outside rate is not applied to winter design
> > > calculations, and 2)Why there is simultaneous heating and cooling
> > > during design day calculations. 
> > 
> > There is simultaneous heating a cooling because the chilled water coil
> > leaving 
> > air setpoint temperature is 12.78C and the heating coil air setpoint 
> > temperature is 37.8C. The coil controls on this system use SET POINT 
> > MANAGER:SCHEDULED, so they have no sensitivity to zone loads. 
> > 
> > Also, the VAV terminal units "SINGLE DUCT:VAV:NOREHEAT" will not vary
> > air flow 
> > rate when there is a heating load in the zone, they will stay at
> minimum
> > flow. 
> > 
> > What type of system are you trying to model? How is it controlled?
> > 
> > Mike
> > 
> > > 
> > > I have uploaded the Input file in the Problem Submittals\MAB3
> folder.
> > > 
> > > Thank you for your support.
> > > 
> > > Merid 
> > > 
> > > 
> > > 
> > > 
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov <http://www.energyplus.gov>
> <http://www.energyplus.gov <http://www.energyplus.gov> > 
> > > 
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> <http://groups.yahoo.com/group/EnergyPlus_Support/> 
> > <http://groups.yahoo.com/group/EnergyPlus_Support/
> <http://groups.yahoo.com/group/EnergyPlus_Support/> > 
> > > 
> > > Attachments are not allowed -- please post any files to the
> > appropriate folder
> > > in the Files area of the Support Web Site.
> > > 
> > > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under
> > the
> > > Documentation link and press the "search" button.
> > > 
> > > Yahoo! Groups Links
> > > 
> > > 
> > > 
> > > 
> > > 
> > 
> > ========================================================
> > Michael J. Witte, GARD Analytics, Inc.
> > EnergyPlus Testing and Support 
> > EnergyPlus-Support@xxxxxxxx <mailto:EnergyPlus-Support%40gard.com>
> <mailto:EnergyPlus-Support%40gard.com> 
> > 
> > 
> > 
> > 
> > 
> > [Non-text portions of this message have been removed]
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov <http://www.energyplus.gov> 
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> <http://groups.yahoo.com/group/EnergyPlus_Support/> 
> > 
> > Attachments are not allowed -- please post any files to the
> appropriate folder
> > in the Files area of the Support Web Site.
> > 
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under
> the
> > Documentation link and press the "search" button.
> > 
> > Yahoo! Groups Links
> > 
> > 
> > 
> > 
> > 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support 
> EnergyPlus-Support@xxxxxxxx <mailto:EnergyPlus-Support%40gard.com> 
> 
> 
> 
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/