[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] SimHVAC: Maximum iterations



There is a known control problem when using more than one ConstantFlow chiller 
(CR7347, fixed for version 2.1).  Take the expidf output file, and change the 
chiller objects to be "VariableFlow" instead of "ConstantFlow".  This should 
get rid of the max iteration errors.  The chilled water loop pump should still 
controll the overall chilled water flow and send excess flow through the bypass 
pipe, so this should be equivalent from an energy perspective.  If this does 
not help, please send the input file to energyplus-support@xxxxxxxx or post it 
in the files area of the yahoo group.

Mike


On 19 Oct 2007 at 14:40, Zhen Tian wrote:

> Dear all,
> 
> I am modeling a building with VAV system. I got lots of warnings: SimHVAC:
> Maximum iterations when I change one big to several small chillers. I changed
> the setting in iterations from 20 to 50 and so on, but I still got these
> warnings.
> 
> I used the compact HVAC to generate the HVAC system. Is there any method to get
> rid of these warnings.
> 
> Thanks a lot.
> 
> Regards,
> 
> David
> 
>  __________________________________________________
> Do You Yahoo!?
> Tired of spam?  Yahoo! Mail has the best spam protection around 
> http://mail.yahoo.com 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/