I've run my own comparison and get a simulated u-value of 3.55 vs. a reported u-
value of 3.57. I used the ConvectionCoefficients object to force the exterior
convection coefficient to the stated nominal value of 25.47 W/m2-K.
See Window U-Value.zip in the Examples folder in the files area of the yahoo
group for inputs, outputs, and comparison spreadsheet.
http://tech.groups.yahoo.com/group/EnergyPlus_Support/files/Examples/Window%20U-
Value.zip
Mike
On 31 Oct 2007 at 9:15, wanglei wrote:
> Dear Mike
>
> I have tried to simulate my model as your suggestion.
>
> I set the IRHemispherical Emissivity : Front side and Back Side as 0.0001
>
>
> The conductance of single-pane system is 3.519 w/m2-K in the EIO file.
>
> The output results is:
> The Window Heat Loss is 490.7W ;
> The Ext Convection Coeff is23.68W/m2-K;
> The Int Convection Coeff is 3.076W/m2-K.
> The Outdoor Dry Bulb is -17.8 oC
> The Zone Mean Air temperature is 21.1
>
> The calculated results of the conductance is 2.68 w/m2-K
>
> By the way, the vaule of skyclearness is 0 in my designDay object so solar
> radiation isn't considered.
>
> I don't know why the calculated results less than the value in the EIO file.
>
> Thanks
>
> Lei Wang
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
> 2007-10-31,"Michael J. Witte" <mjwitte@xxxxxxxx> :
>
>
> I suspect that radiant heat transfer inside and outside are affecting your
> results. Repeat your test with a simple single-pane construction and set the IR
> Hemispherical Emissivity: Front Side (and Back Side) to 0.00001 to supress
> radiant transfer. Does this compare better?
>
> For a double-pane system, you will need to define two instances of the glass,
> one with IR Hemispherical Emissivity: Front Side set to 0.00001 and another with
> IR Hemispherical Emissivity: Back Side set to 0.00001. You need to keep the
> radiant transfer across the window gas active.
>
> Mike
>
> On 30 Oct 2007 at 10:19, wanglei wrote:
>
> > Dear Linda
> >
> >
> > Now I create a single zone model with a south window without Frame and
> > Divide. The window area is 4.5m2.
> >
> > According to the ASHARE winter conditions, I create a HeatDesign Day:
> > The outside temperature is -17.8C
> > The wind speed is 6.71m/s
> >
> > The indoor temperature is 21.
> >
> > After calculating, the Window Heat Loss is 490.7W ; the Ext Convection Coeff
> > is 23.68W/m2-K; the Int Convection Coeff is 3.076W/m2-K.
> >
> > I use the formula k=Q/(tin -tout)/A to calculate the window u value
> >
> > The result is 2.8 W/m2-K. In eio file, this value is 3.785 W/m2-K
> >
> > Could you tell me why these two value isn't equal
> >
> > Thank you
> >
> > Lei wang
> >
> >
> >
> >
> >
> > [Non-text portions of this message have been removed]
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> > Documentation link and press the "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx
>
>
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/