Re: [EnergyPlus_Support] Coil Sizing
Justin,
The central system supply air flow rate is sized on the sum of the zone
design cooling air
flow rates which are based on zone sensible loads. The central cooling
coil chilled water flow rate
is sized on the total coil cooling load, as is the coil UA.
For central DX coils, supply air flow rate is set in the same manner as
for chilled water coils. The cooling
capacity of the DX coil is based on the total cooling load.
Fred Buhl
Justin Wong wrote:
> Hi all,
>
> I understand that air side coil are sized based on the sensible rather
> than total (sensible +latent) load. Is there a work around plan for
> v2.0 or there is an improvement in V2.1?
>
> Thank you very much.
>
> Best Regards,
> Justin
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/