[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] Modeling of a partially cascaded heat pump system
This will be difficult to model. EnergyPlus does not have an air to water heat
pump. For cooling operation, you can use an air cooled chiller with
appropriate performance adjustments. For heating operation, you could use the
heat pump water heater, but this requires modeling a hot water storage tank so
there is extra complexity.
To model the cascaded heat pump, use UnitarySystem:HeatPump:WaterToAir and put
the water side of the heat pump coil(s) in series on the same branch as the
radiant cooling panel, and set both component control types to SERIESACTIVE.
But there are some control issues, and I am not completely sure this will
simulate properly.
Mike
On 9 Nov 2007 at 1:33, zh_guangyu wrote:
> Hello,I am getting started to use E+...the system consists of two or
> more heat pumps,the primary air to water heat pump provide chilled
> water for radiant ceiling,and part of the return water acts as cooling
> water for another small water to air heat pump that only processes
> fresh outside air. ... how to establish the model? Thanks.
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/