[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] V2.0 electric generator - change: baseload to track schedule



As the error file states, you must change the branch control type for 
Branch named: DHW Branch to ACTIVE

   ** Severe  ** plant flows do not resolve -- splitter inlet flow does 
not match mixer outlet flow
   **   ~~~   **  Occurrence info=MIAMI FL UNITED STATES TMY2 12839 
WMO#=722020, 01/02 08:00 - 08:10
   **   ~~~   ** Plant loop name= HOT WATER LOOP
   **   ~~~   ** Plant mixer name= REHEAT MIXER
   **   ~~~   ** Mixer outlet mass flow rate= 43.071512 {kg/s}
   **   ~~~   ** Plant splitter name= REHEAT SPLITTER
   **   ~~~   ** Splitter inlet mass flow rate= 43.000012 {kg/s}
   **   ~~~   ** Check control type for Branches between, components 
that request flow should be ACTIVE control type
   **  Fatal  **  Simulation terminated because of problems in Plant 
Flow Resolver
   ...Summary of Errors that led to program termination:
   ..... Reference severe error count=1
   ..... Last severe error=plant flows do not resolve -- splitter inlet 
flow does not match mixer outlet flow
   ** Warning ** Found potential problem with Control Type for Branch 
named: DHW BRANCH
   **   ~~~   ** This branch should (probably) be ACTIVE but has control 
type PASSIVE


  BRANCH,
    DHW Branch,            !- Branch Name
    0,                       !- Maximum Branch Flow Rate {m3/s}
    WATER USE CONNECTIONS,      !- Comp1 Type
    DHW,                   !- Comp1 Name
    DHW Inlet Node, !- Comp1 Inlet Node Name
    DHW Outlet Node,!- Comp1 Outlet Node Name
->  ACTIVE;                 !- Comp1 Branch Control Type


mapascualb wrote:
>
> Hello:
>
> I have just upload a file to the problem submital area, because I am
> getting a crash when I change the ELECTRIC LOAD CENTER:DISTRIBUTION,
> from BASELOAD to TRACK SCHEDULE.
>
> Thanks for your attention.
>
> Miguel Angel Pascual
>
>  

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/