Hello Richard,

Thanks for the help, that was very usefull.

Best regards,
Ricardo Miranda


2007/11/26, Richard Raustad <RRaustad@xxxxxxxxxxxx>:
>
>   A window air conditioner or packaged terminal air conditioner (PTAC)
> would also work for 1) if it's a single zone. And these models do not
> require a heater and are easier to implement. A packaged terminal heat
> pump (PTHP) could also be used in a single zone, but this model requires
> a heater.
>
> Richard Raustad wrote:
> >
> > 1-If central cooling is typically used for these rooms, use a furnace or
> > unitary system. You would most likely schedule the heating coil off. Be
> > careful to avoid frost build up on the coil (check the supply air
> > temperature). These models were intended to simulate air conditioners
> > for "occupied" zones and have not been tested at low temperatures. You
> > can probably simulate conditions down to about 15C but I'm not sure of
> > the lower limits.
> >
> > 2-The refrigerated case model is based on an empirical model by Howell.
> > This model varies case performance based on room relative humidity or
> > dew point. Interactions of the case with the zone is modeled through
> > case credits. This model is probably not the best choice for simulating
> > a cold room. And this refrigerated case would have to be connected to a
> > refrigeration compressor rack, which is typically not used for walk-in
> > coolers or "cold" rooms found in a super market. The model intent is to
> > simulate various display cases in a super market, other uses would be
> > crude approximations. The refrigerated case model could only be used to
> > "approximate" energy use for isolated and well-insulated walk-in type
> > coolers or freezers. The height input in the refrigerated case object is
> > only for anti-sweat heater calculations (heat balance method). Case
> > performance is based on lineal footage to simulate various case lengths.
> > See the Engineering documentation for equations used and references to
> > papers describing the model.
> >
> > 3-DB should answer this question.
> >
> > The super market (SuperMarket*.idf) example files distributed with
> > Energy+ may also be useful. There is an example of a walk-in freezer,
> > but is only intended to be an example and shows how flexible the
> > refrigerated case model inputs were designed. You must carefully use
> > manufacturers data to get close to the actual energy use for this type
> > of equipment.
> >
> > Ricardo Miranda wrote:
> > >
> > > Hello,
> > >
> > > I´m simulating a supermarket that have some coldrooms. This
> > coldrooms are
> > > supplied by a central cooling and has a different height ( shorter)
> > of the
> > > rest of the building. I have some questions:
> > >
> > > 1- what type of system should we use to refrigerate such rooms?
> > > 2-Can the coldrooms be modeled as a refrigereted case, and if so, how
> > > can we
> > > account for it´s height, since energy plus only account for the linear
> > > lenght and doesn´t have the height option?
> > > 3-If it cannot be modeled as a refrigereted case, using the
> > interface tool
> > > Design builder, how can we model these rooms with a different height
> > > of the
> > > rest of the building?
> > >
> > > Regards,
> > > Ricardo Miranda
> > >
> > > [Non-text portions of this message have been removed]
> > >
> > >
> >
> > --
> > Richard A. Raustad
> > Senior Research Engineer
> > Florida Solar Energy Center
> > University of Central Florida
> > 1679 Clearlake Road
> > Cocoa, FL 32922-5703
> > Phone: (321) 638-1454
> > Fax: (321) 638-1439 or 1010
> > Visit our web site at: http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
>
> >
> > UCF - From Promise to Prominence: Celebrating 40 Years
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
>  
>


[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/