Re: [EnergyPlus_Support] RH out of range
These can be difficult to track down at times. The first step is to add some
hourly REPORT VARIABLEs and report "Zone Air Relative Humidity" and "System
Node Relative Humidity" to see if you can track down where in the system it's
becoming foggy.
Mike
On 5 Dec 2007 at 22:10, Justin Wong wrote:
> Hi all,
>
> I am simulating an office building using the unitary compact HVAC object
> and I have got the following warnings.
>
> ** Warning ** Calculated Relative Humidity out of range (PsyRhFnTdbWPb)
> ** ~~~ ** Occurrence info=BRISBANE - AUS IWEC DATA WMO#=945780,
> 01/02 07:30 - 07:31
> ** ~~~ ** Dry-Bulb= 18.56 Humidity Ratio= 1.397E-002 Calculated
> Relative Humidity (fraction)= 1.04
> ** ~~~ ** Relative Humidity being reset to 1.0
>
> Any idea how to get rid of these warnings? Any input will be appreciated.
>
> Best Regards,
> Justin
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/