Re: [EnergyPlus_Support] DOE-2 and EnergyPlus calculated different cooling loads for the same building



Thank you very much for your reply. Please do not consider my response saying that we used purchased air. The uploaded files are the ones to be considered.
   
  I have another question related with the modelling of light shelves in EnergyPlus. According to the manuals, the part of the lightshelf extending towards outside has to be defined as a 'Surface:Shading:Attached' object, while the part extending towards the interior space is to be defined as a 'Surface:Heat Transfer' object. My question is about the crossection these two pieces of the light shelf come together. Do they touch each other? If they do, then they are actually a single element which will inevitably lead to heat conduction from outside to inside. Especially, if the lightshelf is metal, the problem will be more serious. If the lightshelf is not not actually a single element and it is in fact made up of two pieces(outer and inner piece), then how do these two pieces come together?...or how do EnergyPlus assume their connection? Is it the window itself that stands in between the two parts of the lightshelf and prevents conduction?...in other words, is the window a
 continuous single window that have one outer and one inner lightshelft or are there two windows (upper and lower window) separated by a single lightshelf? Could you explain the cross section these four objects come together (upper window, lower window, outer shelf, inner shelf) in EnergyPlus?
   
  Thanks
  Simge Andolsun  
  
"Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
          You say in your response to Edwin that you used Purchased Air, but that is not 
the case in the uploaded EnergyPlus input files. These have full-blown VAV 
systems. So, it is not clear what is being compared here. Based on a quick 
review of the inputs files, there are two obvious factors. One, the EnergyPlus 
runs are cooling to 25.56C, while the DOE-2 runs are cooling to 25.1 to 25.3C. 
EnergyPlus has no throttling range on the thermostat, while DOE-2 does. Set 
the DOE-2 throttling range as small as possible to achieve closer zone 
temperatures. 

The most likely influence which could produce a near-constant offset in cooling 
loads is the foundation. In the EnergyPlus simulation, the concrete floors are 
exposed to a constant 18C outside surface temperatures. This is not realistic. 
If I remember correctly, in DOE-2, the ground temperatures come from the 
weather files, so it's not clear from these files what temperatures are driving 
the floors in the DOE-2 model. Looking at the EnergyPlus temperature graphs, 
all of the zones are being pulled down to the heating setpoint of 21.1C for one 
or more hours at night. The floors are doing this. I suspect the DOE-2 floors 
have warmer boundary conditions, so that is why the zones do not cool down as 
quickly at night. (Also - note that the floor construction in the DOE-2 file 
is wrong for Space2-1.)

I would also recommend using custom weighting factors in the DOE-2 model to 
avoid the need to guess at floor weights.

Mike

On 7 Dec 2007 at 16:59, Simge Andolsun wrote:

> Please find the attached EnergyPlus(1) and DOE-2(2) files. These two files are
> supposed to be the DOE-2 and EnergyPlus simulations of the same building. Thus,
> they are supposed to exhibit the same cooling energy consumptions. The cooling
> energy consumptions, however, differ. Please find the attached line graph (3)
> that shows the cooling energy consumption of the building with respect to
> EnergyPlus and DOE-2 simulations on the peak cooling day (3rd of July). The
> DOE-2 output exhibited twice of EneryPlus results. Please also find the attached
> line graphs (4) that show the temperature fluctuations in the interior zones of
> DOE-2 and EnergyPlus spaces. When compared to EnergyPlus simulation, there was a
> time-lag in the temperature fluctuations of the DOE-2 interior space. This made
> us consider FLOOR-WEIGHT factor in DOE-2 as a probable reason. We tried
> different floor-weight values. This however did not help much. Moreover, the
> cooling energy graphs (3) showed a very similar
> behavior although the values were very different. This suggested that there
> might be a single definite reason for the difference in cooling loads
> calculated by the two programs. With your experience on EnergyPlus, which input
> would you recommend us to check as the probable reason for the difference in
> results?
> 
> Thanks in advance for your reply,
> ps: If I should upload the attached files, please let me know.
> 
> Simge Andolsun 
> Graduate Research Assistant
> Texas A&M University
> Energy Systems Laboratory
> 
> 
> ---------------------------------
> Never miss a thing. Make Yahoo your homepage.
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 

========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support 
EnergyPlus-Support@xxxxxxxx



                         

       
---------------------------------
Be a better friend, newshound, and know-it-all with Yahoo! Mobile.  Try it now.

[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/