RE: [EnergyPlus_Support] DOE-2 and EnergyPlus calculated different cooling loads for the same building
You can also look at the testing reports on the EnergyPlus web
site--they compare EnergyPlus with DOE-2.1E, BLAST and other results.
________________________________
From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Michael J.
Witte
Sent: Monday, December 10, 2007 4:21 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] DOE-2 and EnergyPlus calculated
different cooling loads for the same building
You say in your response to Edwin that you used Purchased Air, but that
is not
the case in the uploaded EnergyPlus input files. These have full-blown
VAV
systems. So, it is not clear what is being compared here. Based on a
quick
review of the inputs files, there are two obvious factors. One, the
EnergyPlus
runs are cooling to 25.56C, while the DOE-2 runs are cooling to 25.1 to
25.3C.
EnergyPlus has no throttling range on the thermostat, while DOE-2 does.
Set
the DOE-2 throttling range as small as possible to achieve closer zone
temperatures.
The most likely influence which could produce a near-constant offset in
cooling
loads is the foundation. In the EnergyPlus simulation, the concrete
floors are
exposed to a constant 18C outside surface temperatures. This is not
realistic.
If I remember correctly, in DOE-2, the ground temperatures come from the
weather files, so it's not clear from these files what temperatures are
driving
the floors in the DOE-2 model. Looking at the EnergyPlus temperature
graphs,
all of the zones are being pulled down to the heating setpoint of 21.1C
for one
or more hours at night. The floors are doing this. I suspect the DOE-2
floors
have warmer boundary conditions, so that is why the zones do not cool
down as
quickly at night. (Also - note that the floor construction in the DOE-2
file
is wrong for Space2-1.)
I would also recommend using custom weighting factors in the DOE-2 model
to
avoid the need to guess at floor weights.
Mike
On 7 Dec 2007 at 16:59, Simge Andolsun wrote:
> Please find the attached EnergyPlus(1) and DOE-2(2) files. These two
files are
> supposed to be the DOE-2 and EnergyPlus simulations of the same
building. Thus,
> they are supposed to exhibit the same cooling energy consumptions. The
cooling
> energy consumptions, however, differ. Please find the attached line
graph (3)
> that shows the cooling energy consumption of the building with respect
to
> EnergyPlus and DOE-2 simulations on the peak cooling day (3rd of
July). The
> DOE-2 output exhibited twice of EneryPlus results. Please also find
the attached
> line graphs (4) that show the temperature fluctuations in the interior
zones of
> DOE-2 and EnergyPlus spaces. When compared to EnergyPlus simulation,
there was a
> time-lag in the temperature fluctuations of the DOE-2 interior space.
This made
> us consider FLOOR-WEIGHT factor in DOE-2 as a probable reason. We
tried
> different floor-weight values. This however did not help much.
Moreover, the
> cooling energy graphs (3) showed a very similar
> behavior although the values were very different. This suggested that
there
> might be a single definite reason for the difference in cooling loads
> calculated by the two programs. With your experience on EnergyPlus,
which input
> would you recommend us to check as the probable reason for the
difference in
> results?
>
> Thanks in advance for your reply,
> ps: If I should upload the attached files, please let me know.
>
> Simge Andolsun
> Graduate Research Assistant
> Texas A&M University
> Energy Systems Laboratory
>
>
> ---------------------------------
> Never miss a thing. Make Yahoo your homepage.
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov <http://www.energyplus.gov>
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
<http://groups.yahoo.com/group/EnergyPlus_Support/>
>
> Attachments are not allowed -- please post any files to the
appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under
the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx <mailto:EnergyPlus-Support%40gard.com>
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/