[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] Hydbrid control and compact hvac
If you look at the example file HybridVentilationControl.idf, you will see that
there are two system availability manager. One that is listed in the air
primary loop's availability manager list (this will be generated by the COMPACT
HVAC expander) and then there is a SYSTEM AVAILABILITY MANAGER:HYBRID
VENTILATION CONTROL object which stands by itself and is not referenced in any
list. So it should work to simply add a SYSTEM AVAILABILITY MANAGER:HYBRID
VENTILATION CONTROL object to the base idf file which contains the COMPACT HVAC
objects.
Mike
On 16 Dec 2007 at 11:37, Justin Wong wrote:
> Hi all,
>
> I'm trying to simulate a building using mixed mode. Is it possible to
> use the hybrid control manager to switch off the supply air fan in
> compactHVAC:System:Unitary or do I have to resort to using the expanded
> version?
>
> Many thanks for your comments.
>
> Best Regards,
> Justin
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/