[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
RE: [EnergyPlus_Support] Window Heat Gain of South oriented window
Craig has explained the solar aspect.
Another factor is that you said the zone is free-floating with no heating or
cooling. If you are reporting window heat gains, these report the net impact
of both the transmitted solar gains and conduction gains/losses through the
glass. Floating zone temperatures may cloud the comparison between summer and
winter. A better comparison would be to report transmitted solar rather than
window heat gain, or to add Purchased Air (COMPACT HVAC:ZONE:PURCHASED AIR) to
control the zone to a constant indoor temperature.
Mike
On 27 Dec 2007 at 22:07, Christensen, Craig wrote:
> If I understand correctly what you describe in your email then ... yes,
> these results are normal and explainable.
>
>
>
> In the summer (for a northern latitude), the sun passes high overhead
> and solar radiation strikes a south-facing window at a very oblique
> angle. Therefore, the intensity of the incident radiation is
> significantly reduced (the direct beam radiation is multiplied by the
> cosine of the incidence angle). Window heat gains also depend on the
> sky diffuse and ground-reflected radiation and the reflection,
> absorption, and transmission of the radiation as it passes through the
> window glass, but the effect of sun angle on the incident radiation is
> the dominant effect in the month-to-month variation (see the figure).
> The fact that south-facing windows have higher gains in winter and lower
> gains in summer is a key principle for passive solar heating of
> buildings. Shading devices above south windows (overhangs) also take
> advantage of high sun angles to provide summer shading and further
> reduction of window heat gains.
>
>
>
> Craig
>
>
>
>
>
>
>
>
>
>
>
> ________________________________
>
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of anarui.oliveira
> Sent: Wednesday, December 26, 2007 11:31 AM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Window Heat Gain of South oriented window
>
>
>
> Greetings!
> I'm just starting now with E+ and I tried out some basic configurations
> (basicaly a box with a window) in "free" simulation mode (no heating or
> cooling) which returned some awkward results:
> - A south oriented window, with no shading of any type, returned lower
> Window Heat Gains in a Summer Week than in a Winter Week (I checked the
> Direct and Difuse Solar and they are lower in Winter, as would be
> expected);
> - And also the same window returns larger Window Heat Gains as I a
> rotate the exact same building (rotation relative to the North) as to
> rotate the window to East or West (as I rotate the building, the
> strange Summer-Winter behaviour also diminishes and eventually
> vanishes);
> Are these results in any way normal or explainable? Any idea what I
> might be doing wrong?
> I appreciate all help I can get. Thanks!
>
>
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/