See responses below. MJW
On 27 Dec 2007 at 10:32, Zhen Tian wrote:
> 1. The compact HVAC chilled water loop does not allow variable flow for both
> primary and decondary, it only allows varible+constant or constant+variable.
Because Compact HVAC currently supports only one chilled water setpoint,
"Variable Flow No Secondary" is equivalent to variable+variable. The flow in
the demand-side (where the coils are) will be the same as the flow in the
supply side (where the chiller is).
> 2. When I create two separate chilled water loops. I will create two chillers.
> How can I create two chilled water loops with only one chiller?
>
This is not supported.
Mike
> Thanks a lot for your help.
>
> Regards,
>
> Zhen
>
> "Michael J. Witte" <mjwitte@xxxxxxxx> wrote: If
> you want to create two separate chilled water loops using COMPACT HVAC, you
> must make two different idf files, and then merge them expidf files by hand
> using a text editor.
>
> For this particular application, it may work for you to use COMPACT HVAC to
> create a chilled water loop serving the cooling coils with variable flow
> primary and variable flow secondary. Then, using the expidf file, add LOW TEMP
> RADIANT SYSTEM:CONSTANT FLOW to the simulation.
>
> Mike
>
> On 20 Dec 2007 at 11:02, Zhen Tian wrote:
>
> > Dear all,
> >
> > I have a question about the configuration of primary and secondary chilled
> water > loops. > > The primary chilled water loop has variable flow pump.
> Connected secondary loops > have two pumps, one constant flow pump for radiant
> panels and one variable flow > pump for cooling coils. In the compact HVAC, it
> does not allow two chilled water > loops. Does anyone has experience how to
> arrange this configuration? > > Thanks a lot in advance. > > Regards, > > David
> > > > --------------------------------- > Looking for last minute shopping
> deals? Find them fast with Yahoo! Search. > > [Non-text portions of this
> message have been removed] > > > > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov > > The group web site is: >
> http://groups.yahoo.com/group/EnergyPlus_Support/ > > Attachments are not
> allowed -- please post any files to the appropriate folder > in the Files area
> of the Support Web Site. > > EnergyPlus Documentation is searchable. Open
> EPlusMainMenu.pdf under the > Documentation link and press the "search" button.
> > > Yahoo! Groups Links > > > > >
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx
>
>
>
>
>
>
> ---------------------------------
> Be a better friend, newshound, and know-it-all with Yahoo! Mobile. Try it now.
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/