Re: [EnergyPlus_Support] Ice Storage Tank
I am not sure if the ice storage model will support this, but here is a
suggestion to try. Using the PLANT OPERATION SCHEMES object for the chilled
water loop, specify COMPONENT SETPOINT BASED OPERATION with a schedule that is
1 during unoccupied hours and 0 during occupied hours, then specify COOLING
LOAD RANGE BASED OPERATION with a schedule that is 1 during occupied hours. In
the PLANT LOOP object, set the "Load Distribution Scheme" field to optimal or
sequential or uniform as desired.
Mike
On 3 Jan 2008 at 16:37, Ricardo Miranda wrote:
> Hello,
>
>
> I´m doing a simulation of a building that have a ice storage tank.
> During the building occupation time (during the day) the ice tanks work with a
> chiller and during the night the tank is charged. The chiller is in parallel
> with ice bank when the storage is not being charged. I´m already implemented
> that in the cooling plant with two chiller objects representing the chiller in
> the real plant, one upstream and the other in a branch paralell with the storage
> tank but now I don´t know how control the plant loop, to during the day work
> both the chiller and storage ice tank and work only the chiller when the tank
> lost his cooling capacity.
>
> Can you help me?
>
> Best Regards,
> Ricardo Miranda
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/