[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] Control of OnOff Fan
The EnergyPlus fan coil model does not support cycling fans. It only models
continuous fans. The fans are on when the availability schedule is >0, off
when the availability schedule =0. The zone thermostat has no impact on fan
operation, it only controls the heating and cooling coils.
Mike
On 7 Jan 2008 at 17:10, anarui.oliveira wrote:
> Hello.
> For the system I created with Compact: HVAC: Fan Coil (I'm already
> working with the expanded file):
> - If I want to shut off the fan when no heating or cooling is required,
> can I use Fan: Simple: OnOff ?
> - I tried to create this alternative object (I assigned it the same
> nodes as were defined in the default Fan: Simple: ConstVolume object)
> and substitute it into the Fan Coil: 4 pipe,
> - but I can't understand, from the Help files, waht is the principle to
> actually control the fan so as to make it turn off when no
> cooling/heating is necessary.
> Can you help me?
>
> Regards,
> Ana Rui.
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/