RE: [EnergyPlus_Support] Re: Report Variable Errors
For the correct variable names in your run, look at the .rdd and .mdd files.
You will need to put in a:
Report, Variable Dictionary, IDF;
command and it will produce in proper IDF form.
If you have an HVAC system, your zone temperatures should be
following the set points. If you don't have an HVAC system, then you
shouldn't be seeing cooling loads. Heat Gains and losses, yes, but
not cooling loads. Maybe you have a purchased air system? (this is
what we use to see the heating / cooling loads without restrictions
of actual HVAC systems.)
At 05:19 PM 1/20/2008, Danny Bishop wrote:
>That leads me to another question. Now, as expected, the temperatures in the
>zones are basically doing their own thing independent of any HVAC, but I
>still get large Cooling loads. Do you know what the cooling/heating load
>represents? Also, where is the list of correct variable names?
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/