Re: [EnergyPlus_Support] problem in assigning AirflowNetworkComponent: The opening to a window
Neslihan:
The surfaces used in the AirflowNetwork:MultiZone:Surface, which specify a
linkage as the AirflowNetwork:Multizone:Component Detailed opening object,
require surface types as door, window, or glass door. Other surface types
are not allowed. A paragraph is extracted from the Input Output Reference on
page 656:
AirflowNetwork:Multizone:Component Detailed Opening
This object specifies the properties of air flow through windows and doors
(window, door and glass door heat transfer subsurfaces) when they are closed
or open. The fields are similar to those for AirflowNetwork:Multizone:
Surface Crack Data when the window or door is closed, but additional fields
are required to describe the air flow characteristics when the window or
door is open. These additional fields include opening type, opening
dimensions, degree of opening, and opening schedule.
The surfaces names (ON DUVAR and ARKA DUVAR) defined in the
AirflowNetwork:MultiZone:Surface in your input are referred to the "wall"
type. That is why severe errors are provided.
In addition, enclosed is my reply to you on Jan. 7, 2008. The two issues are
not addressed.
Thanks.
Lixing
Enclosed:
Neslihan:
I looked at the input file and found two issues using the AirflowNetwork
model.
1 Parent surface facing
Any parent surface defined as an AIRFLOWNETWORK:MULTIZONE:SURFACE does not
allow the parent surface faces itself: the user supplied surface name =
OutsideFaceEnviroment object. The reason to reject this choice is that the
prarent surface has to face different interior and exterior boundary
conditions, so that the AirflowNetwork model can work. A severe error
message in the eplusout.err shows it.
2 Wind direction
Wind direction fields used in the AIRFLOWNETWORK:MULTIZONE:WIND PRESSURE
COEFFICIENT ARRAY object do not allow the repeated values. The object is
enclosed.
As long as you make the above two issues correct, the AirflowNetwork model
should work. However, you still have other warning issues.
Best regards,
Lixing
!- =========== ALL OBJECTS IN CLASS: AIRFLOWNETWORK:MULTIZONE:WIND PRESSURE
COEFFICIENT ARRAY ===========
AIRFLOWNETWORK:MULTIZONE:WIND PRESSURE COEFFICIENT ARRAY,
basinc-array-ön, !- WPC Array Name
10, !- Reference Height for WPC Data {m}
180, !- Wind Direction #1 {deg}
180, !- Wind Direction #2 {deg}
180, !- Wind Direction #3 {deg}
180, !- Wind Direction #4 {deg}
180, !- Wind Direction #5 {deg}
180, !- Wind Direction #6 {deg}
180, !- Wind Direction #7 {deg}
180, !- Wind Direction #8 {deg}
180, !- Wind Direction #9 {deg}
180, !- Wind Direction #10 {deg}
180, !- Wind Direction #11 {deg}
180, !- Wind Direction #12 {deg}
180, !- Wind Direction #13 {deg}
180, !- Wind Direction #14 {deg}
180; !- Wind Direction #15 {deg}
----- Original Message -----
From: "neslihanturkmenoglu" <neslihanturkmenoglu@xxxxxxxxx>
To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Wednesday, January 23, 2008 8:08 AM
Subject: [EnergyPlus_Support] problem in assigning AirflowNetworkComponent:
The opening to a window
> hi
> I've uploaded my file.
> program gives errors as;
> ** Severe ** GetAirflowNetworkInput: AirflowNetworkComponent: The
> opening must be assigned to a window, door or glassdoor at ON DUVAR
> ** Severe ** GetAirflowNetworkInput: AirflowNetworkComponent: The
> opening must be assigned to a window, door or glassdoor at ARKA DUVAR
> but I ve already defined assigned the 2 simple openings to 2 front and
> back window. What do I do wrong?
> thank you very much
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/