[EnergyPlus_Support] Re: U value input



Many thanks Brent. 

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Griffith, Brent" 
<brent_griffith@...> wrote:
>
> I don't quite follow you, I ran your files and they seem to be 
reporting
> similarly.  If you are looking at the Envelope Summary in the html
> report, there does seem to be a problem with reporting of "U 
Factor with
> Film".  
> 
>  
> 
> But in general, the best approach is to use the E+ report for U-
values
> without the film coefficients and then apply the film coefficients
> yourself so that they agree with what the Standard is expecting.
> Internally E+ doesn't use crude combined convection/radiation film
> coefficients so reporting with the film coefficients is somewhat
> arbitrary.  E+ is neutral with respect to specific Standards and 
it may
> be that there are different film coefficients that need to be used
> depending on the Standard.  
> 
>  
> 
> It is important to understand that film coefficients, and hence U-
values
> with film coefficients, depend on orientation (vertical, 
horizontal heat
> flow up, horizontal heat flow down, etc) and are not uniquely 
defined
> for just constructions.  So the reporting of these is by surface, 
not by
> construction.  To get a report in eio file with film coefficients 
you
> would need to add a "Report, surfaces, details;" input object to 
the idf
> file.  See page 23 (or 29 absolute) in 
OutputDetailsAndExamples.pdf for
> more information.
> 
>  
> 
> ________________________________
> 
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of 
eric_zhou1223
> Sent: Tuesday, January 22, 2008 10:55 PM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Re: U value input
> 
>  
> 
> Thanks a lot, Brent. I used the tool to output two files, the only 
> difference between them being location and perhaps system type. 
Yet 
> one of them can report "U-Factor with Film " and "U-Factor no 
Film", 
> another can only report "U-Factor no Film". Would you please give 
> me hint on this? Thanks again. I uploaded two files package 
named "U 
> factor".
> 
> Eric
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> , "Griffith, Brent" 
> <brent_griffith@> wrote:
> >
> > Not directly. E+ uses layer-by-layer descriptions and targeting a
> > specific U-value often requires iteration. Tune the material 
> properties
> > of an insulation layer inside the construction. Be careful about 
> the
> > surface film coefficients when setting targets... (E+ can report 
> them
> > with or without, but Standards aren't always so clear). If the 
> Standard
> > is 90.1, you could try constructions out of an input file from 
the
> > EnergyPlus Example File Generator. 
> > 
> > 
> > 
> > ________________________________
> > 
> > From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> 
> > [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> ] On Behalf Of 
> eric_zhou1223
> > Sent: Thursday, January 17, 2008 12:27 AM
> > To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> 
> > Subject: [EnergyPlus_Support] U value input
> > 
> > 
> > 
> > Hi all,
> > 
> > Is there a simple way to define an U value for a wall,which is 
> made of 
> > several layers, like in eQuest? Given that I need to set the 
wall 
> U-
> > value to a standard value.
> > 
> > Eric
> > 
> > 
> > 
> > 
> > 
> > [Non-text portions of this message have been removed]
> >
> 
>  
> 
> 
> 
> [Non-text portions of this message have been removed]
>




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/