It seems the main problem is the primary-secondary system for chilled
water loop. If you change "chilled water pump configuration"  from
"constant primary variable secondary" to "variable flow no secondary"
, at least the model can run for a whole year although there are still
some severe errors.  

For the severe error of "FindRootSimpleController: Controller error
for controller", I do not know how to fix them.  One possible reason
is that chiller capacity or cooling coil capacity is not sufficient. 

For primary-secondary system in E+, you may try to use another option
"plant connection component". 

Hope it helps.

Tj Ywh

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "eric_zhou1223"
<eric_zhou1223@...> wrote:
>
> 
> This kind of warnings accumulated up to more than 30000 and 
> terminated the program:
> 
>    **  Fatal  ** PlantFlowResolver: Previous condition for Plant 
> Loop=CHILLED WATER LOOP CHILLED WATER LOOP, Branch=VAV SYS WS PREM 
> COOLING COIL CHW BRANCH(>30,000 Out of Bounds errors) causes 
> termination.
> 
> Where can I start to fix it? Your help would be appreciated much.
> Please see the CompactObjectExm.idf in the submital zone.
> 
> Eric
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "eric_zhou1223" 
> <eric_zhou1223@> wrote:
> >
> > Hi all,
> > 
> > I made an IDF file through the CompactHVAC and came across some 
> > warnings as below, while the file was completed successfully 
> anyway. 
> > Anybody could tell me what does they imply and how can I fix them? 
> > Thank you in advance.
> > 
> > 
> >   ** Warning ** PlantFlowResolver: Branch flow rates out of 
> bounds, 
> > for Plant Loop=CHILLED WATER LOOP CHILLED WATER LOOP, Branch=VAV 
> > SYS  WS CORE COOLING COIL CHW BRANCH
> >    **   ~~~   ** Conditions should be: 18.275 <= 4.569 <= 7.193 
> > Occurrence info=SHANGHAI SHANGHAI CHN CUSTOM-583620 WMO#=583620, 
> > 08/01 07:00 - 07:15
> >    
> >   ..............................
> >   
> >      *************  ** Warning ** PlantFlowResolver: 
> > Continuing...Branch flow rates out of bounds, for Plant 
> Loop=CHILLED 
> > WATER LOOP CHILLED WATER LOOP, Branch=VAV SYS  WS CORE COOLING 
> COIL 
> > CHW BRANCH
> >    *************  **   ~~~   **   This error occurred 713 times.
> >    *************  **   ~~~   **   Max=5.708322  Min=4.568808
> > 
> > 
> > 
> > Eric
> >
>




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/