[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Air Flow between Zones



Airflownetwork has limitations which prevent it from being used for this 
application.  This can be modeled as follows:

1.  In the central zone, add a ZONE EXHAUST FAN with a flow rate equal to the 
amount of air which passes to the adjacent zones.  This will balance the 
airflows for the central zone (return = supply - exhaust).  Why put the exhaust 
(extractioni fan) in the central zone?  Because the air loop simulation needs 
to know that some quantity of air is leaving the central zone through a path 
that is not the return duct.  It does not matter if the air leaves through an 
exhaust fan, a door to and adjacent zone, or whatever.

2.  Use MIXING objects to move air from the central zone to the adjacent zones. 
 So, you may ask, why no exhaust fan in the adjacent zones?  When MIXING adds 
air to a zone, it assumes that an equal amount of air has left the zone.  It 
does not matter where the air went.  So, the "extraction" of air from the 
adjacent zones is already modeled.  The extractino fan power can be accounted 
for in the central zone exhaust fan.

Note that the air loop simulation is not aware of the MIXING objects in terms 
of balancing airflow.  It is the user's responsbility to make sure that the 
flow rates are balanced.

Mike


On 17 Jan 2008 at 13:53, Filipe madureira wrote:

> Hi all,
> 
> 
> 
> I working in a commercial building which has the following characteristics:
> 
> 
> 
> 1.       A central zone rounded by several adjacent zones 
> 
> 2.       The adjacent zones communicate with central zone through doors.
> 
> 3.       A central system (CV or VAV, it isn? t defined yet) provides
> treated  fresh (outside)  air to central zone. The air flow rate  accounts
> with the necessary fresh air to central  and adjacent zones 
> 
> 4.       It is planned that adjacent zones have negative pressure  in a way that
> the compensating air flow rate come from central zone through the door (an
> extraction fan will exhaust an air flow rate equal to the fresh air needed in
> the zone ). Adjacent zones will also have a zone forced air unit to provide the
> necessary local  heating or cooling.
> 
> 
> 
> Is it possible to simulate this situation? I?m not sure if I can do this
> with Airflow NetWork . 
> 
> 
> 
> One of my issues is that in the central air loop:
> 
> Return air flow rate + Zone exhaust Flow rate= Supply air flow rate
> 
> 
> 
> so I don? t know if air loop could take in account the air flow rate that
> passes to adjacent zones 
> 
> 
> 
> Thanks in advance for your help
> 
> Best Regards
> 
> 
> 
> Filipe Madureira
> 
> Tel: +351 919 293 876 | E-mail: filipe.madureira@xxxxxxxxxxxxx
> 
> __________________________________________________________________
> 
> FluidInova, Engenharia de Fluidos, SA
> 
> TECMAIA - Parque de Ciência e Tecnologia da Maia
> 
> Rua Engº Frederico Ulrich, nº 2650  |  4470-605 Moreira da Maia | Portugal
> 
> 
> Tel: (351) 229 408 265  |  Fax: (351) 229 408 266
> 
> E-mail:  <mailto:geral@xxxxxxxxxxxxx> geral@xxxxxxxxxxxxx  | Web:
> <http://www.fluidinova.pt/> http://www.fluidinova.pt/
> 
> 
> 
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/