Re: [EnergyPlus_Support] Error with cooling coils



If the error occured only once or just a small number of times, then you can 
ignore it.  If you are using SETPOINT MANAGER:OUTSIDE AIR to reset the chilled 
water temperature as a function of outdoor dry bulb temp, then there is a known 
problem which can cause these error to occur, but only for a few iterations 
early in the simulation which should not impact the results at all.

Mike
 

On 4 Feb 2008 at 12:57, Zhen Tian wrote:

> Dear all,
> 
> I had the following error when I modeled 2 VAV systems with radiant cooling.
> Among them, one VAV systems reported the the error below. Although two air
> systems has the same configuration. Only one VAV system has this error. Both the
> cooling coils are set as "reverse" action.
> 
> The simulation can get run through to the end with results. I am wondering
> whether this error matter to my simulation result and I can just ignore it.
> 
> Thanks.
> 
> Regards,
> 
> David
> 
> ** Severe  ** FindRootSimpleController: Controller error for controller = AHU1
> COOLING COIL CONTROLLER
>    **   ~~~   **  Occurrence info=CALGARY INT'L AB CAN WYEC2-B-25110
>    WMO#=718770, 01/13 14:39 - 14:40 **   ~~~   **   Controller function is
>    inconsistent with user specified controller action = Reverse action **   ~~~ 
>     **   Actuator will be set to maximum action **   ~~~   ** Controller control
>    type=Temperature **   ~~~   ** Controller temperature set point = 17.20 [C]
>    **   ~~~   ** Controller sensed temperature = 17.60 [C] **   ~~~   **
>    Controller actuator mass flow rate set to 2.29 [kg/s] **   ~~~   **
>    Controller actuator temperature = 18.89 [C] **   ~~~   **   Note: Chilled
>    water coils should be reverse action and the entering chilled **   ~~~   **  
>          water temperature (controller actuator temperature) should be below the
>    setpoint temperature **   ~~~   **   Note: Hot water coils should be normal
>    action and the entering hot **   ~~~   **         water temperature
>    (controller actuator temperature) should be above the setpoint temperature
> 
> ---------------------------------
> Looking for last minute shopping deals?  Find them fast with Yahoo! Search.
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/